Neutral wire--help please

19 years ago

I have read on this forum a few times that it is helpful to add a third wire to all of the new home wiring for any future lighting control system. Is there a name for this wire? What do I tell the electrician? What would be an approximate cost for this extra wiring for a 2400 sq ft home. thanks

Comments (10)

  • 19 years ago

    You should tell him that all switch boxes should have a neutral for future electronic controls.

  • 19 years ago

    But... my "we don't do it that way" alarm is going off. I suspect that you'll tell him to put the neutral in, he'll nod his head "yes", and still won't do it, because that's not what he usually does. You'll have to make sure somebody physically checks the first few he does to make sure it really happens.

  • 19 years ago

    Sorry to keep making new posts to add detail... (where is that doggoned "Edit" button?!!!)

    This is important: You don't "tell" him this. This must be in writing, in the signed contract documents.

    (There are hundreds, probably thousands, of threads on this board where "I told him to [fill in the blank], and he didn't do it." "Was it in writing?" "No." "Well then, you're out of luck.")

  • 19 years ago

    thank you so much for your help. I emailed the request to my builder. He says it would be very expensive--few thousand dollars for about 3000 sq ft home. Does that sound right?

  • 19 years ago

    No. But he will charge whatever he will.

  • 19 years ago

    Do you see yourself needing or wanting electronic lighting control in the future? If not, it's probably not worth any extra cost; just let your contractor do what he normally does.

  • 19 years ago

    I really don't understand the reasoning behind this, but let me ask you this...if all you are after is an extra wire, couldn't you run 12/3 or 14/3 instead of /2 then color code the red wire to neutral when necessary? How in the world could that add up to thousands of dollars?

  • 19 years ago

    The red wire of a cable assembly cannot be relabeled as a neutral. That is a violation of the NEC.

    If the electrician will run his hot feed wires to the switch boxes and not to the light fixtures, you will have a neutral present at all switches. He will have to "carry his neutral" on 3way switch legs for this to work, and there will not be a constant hot at each 3way (or 4way).

  • 19 years ago

    Thanks normel...that makes sense.

  • 19 years ago

    There is no need to relabel anything to carry a neutral. You use the white wire in an x/3 cable as the neutral.

    To prewire for future electronic switching, you don't really need to carry the neutral along between switches in 3- and 4-way switching. When you upgrade to electronic switching, the x/3 cables originally installed between the switches are more than sufficient, because you only need two circuit conductors to run a hot and a neutral to each electronic switch.

    In the case Normel describes where the electrican "carries his neutral" between 3- and 4-way switches, the upgrade to electronic switching is again simple--the white wire remains neutral, you connect the black wire as a constant hot, and you cap off the red wire because it is unused.

    To summarize the last couple of confusing paragraphs, and some things other posters have already said: The only place where the electrician has to do anything different than what he would normally do is for a "switch leg" where power first goes to the box for the light fixture, and then a "switch leg" continues on to the switch box. In this case, he needs to run 14/3 or 12/3 for the switch leg, using the black and red wires as the supply and switched wires, and the white wire as a capped-off neutral. (I would suggest consistently using black as the supply, and red as the switched conductor. But that's just a nit.)

    For the travelers between 3-way and 4-way switches, nothing changes from normal practice, because there are always sufficient wires in appropriate colors to reconnect them for electronic controls.* Also, nothing changes for the case where power first goes to the switch, and then on to the light, because you obviously already have a neutral at the switch.

    (*This is the case for normal residential wiring with Romex or other cable. The very rare cases where wiring is in conduit are somewhat different.)