panel grounding question

19 years ago

I have a 200 amp breaker panel.

I have the ground rods outside, but the electrician who installed it (5 years ago) did not connect to the water pipe near the water meter.

Since reading this forum I understand since the pipe is copper from the street the ground wire must connect within five feet of where the pipe enters the house. I have enough green # 6 thwn wire to reach.

Now I talked with 4 electricians for estimates to fix this and got 4 different answers:

Electrician 1: use #6 green THHN since the new code cycle would require it (something about bare copper making burn marks where stapled to wood).

Electrician 2: #6 is acceptable and guess THHN would work.

Electrician 3: use #4 bare copper for the run to the water meter

Electrician 4: Use #4 bare copper and use #6 (it could be green jacketed or bare copper, didnt matter)for the outside ground rods and as a jumper at the hot water tank.

It will be a couple days before I can get to the library to dig a up a copy of the NEC. My question is who do I believe and what code section (table?) covers this. Is it #4 or # wire thats required and does code care one way or another if its bare copper or green jacketed THHN?