w0lley32

switch loop with 14/3 to feed from switch still allowed?

18 years ago

Hi! I am helping my brother to remodel his basement in a house that was built in 1969. I noticed that the upper level of his bungalow was wired by feeding the power to the ceiling light fixture box first, then they distribute from the fixture to other outlets and/or another room, and they run a 14/3 to the switch (switch is not a 3-way switch), and use the red to switch the fixture. The black from the 14/3 is wire-nutted to a pigtail for the switch and the black from another cable (14/2) to go feed another room or an outlet on the same wall. The neutrals are of course all tied together at the switch and at the fixture box.

I am very familiar with electrical work and it is a wiring method that I have encountered frequently, but I don't seem to see it anymore in more recent houses.

I was thinking of using this method to rewire my brother's basement since it allows for less connections and with less connections less chance for one to get loose or heat up, and it also seems that it needs a bit less cable this way. Also, if it is still allowed, can you have more than one of these switch loops on the same circuit? All the houses I have worked on before always had only one per circuit.

Thanks in advance!

Comments (10)

  • 18 years ago

    I like the setup, this gives you a neutral at the switch and also continues the run for close receptacles.

    Skapare; the red and black constitute the switch leg, the remaining wire is the neutral which continues to the next receptacle along with the black.

  • 18 years ago

    Hi! Maybe what I was trying to describe is not called a switch loop. Maybe I should have given an example of what I am talking about. Let's take my brother's "den + 2 bedrooms" circuit. The power comes from the panel to the ceiling fixture box via a 14/2 loomex. From there another 14/2 loomex goes to feed the outlets in the den, and another 14/2 loomex goes to bedroom #1. Also, a 14/3 loomex (bare ground + white + black + red) goes to the switch for the den light. At the fixture box, the whites are wire nutted together, and the bare grounds as well, which are also attached to the box and has a pigtail for the fixture. The blacks are wire-nutted together and the red wire (from the switch) is alone. The hot wire from the chandelier is connected to the red wire and of course the neutral from the chandelier goes to the whites marretted together. The hot black wires are just standing there.

    Then at the switch (which is mounted on the wall separating the den from bedroom #2), there is the 14/3 from the light fixture box and another 14/2 loomex that goes to bedroom #2. In the den switch box, all grounds are wire-nutted together and attached to the box, all whites (neutrals) are wire-nutted together and the two blacks are wire-nutted together with a pigtail that gets attached to the switch. The other leg of the switch is attached to the red wire that goes to the chandelier.

    I hope this description makes it clear. Please note that I live in Montreal Canada and I have seen this wiring technique at my aunt's house (built 1964) and also at other friend's houses where I helped with wiring or installing light fixtures.

    Can someone please tell me if it is still allowed, and if I can use more than one fixture wired this way per branch circuit? Thanks a lot.

  • 18 years ago

    What you have is perfectly legal and common. In Canada our limit is only 12 devices for every branch circuit.

  • 18 years ago

    w0lley32, perfectly legal and a pretty good way of doing things.

    I'm known for using more /3 cable than /2 :)

  • 18 years ago

    Nothing wrong with that wiring method. The method that uses the least amount of cable is the one I like best.

  • 18 years ago

    If you are connecting receptacles to the switch box, which would make sense if they are close to the switch, then sure, you need the neutral in that case, and it would make sense for the red wire to feed back to the light fixture (via the same cable or conduit). I could not tell exactly what was being done from the original wording.

  • 18 years ago

    Thank you guys for your help! Bigbird, when you say I am limited to 12 devices, is the switch counted as a "device"?

  • 18 years ago

    No, only electrical loads such as lights and duplex receptacles are counted as devices for the limit of 12.

  • 18 years ago

    Just don't forget that with this method of wiring you always have HOT at the light fixture. So be careful what you touch. Of course we all know that anyone working on anything electrical would always turn off the power at the main panel!