suplementary ground electrode

20 years ago

i recently installed a cctv camera system with a 160 gb digital vidieo recorder in a friends house.Upon completion i tested the three prong recepticle and it read open ground.The house has two wire,no ground romex.She paid a electrician to replace her 2 prongs to three proung outlets.The bedroom feeds from bathroom where he installed a gfci so he put the gfci protected sticker on the outlet covers. I think these should have also said open ground. Would have saved me some grief and trying to explain to her it is not safe for her EGUIPMENT. so i came back and ran a#12 stranded insulated green safety ground from oulet up through wall, through split level attic down to service panel (finished ceiling below)not a pleasant way to spend several hours.I am NOT a electrician.A guy at work said i could have just (hooked) the ground wire to a cold water pipe and went home,I guess i could have but i do not think that would create a proper ground path,Would the breaker trip wired like he suggested? also while i was there, i drove 2, 8 foot ground electrodes to supplement her waterpipe grounding.Should i use #6 gec to connect or (bond) this to the nuetral or shoud this go to the water pipe as well,this connection is a couple inches from where the pipe enters the foundation.The more i read on bonding and grounding the more confused i get. Thanks joe

Comments (5)

  • 19 years ago

    It should say "NO EQUIPMENT GROUND" .

    If these were existing receptacles, it's marginally dubious that he did this. If he specifically extended the bathroom GFCI circuit to accomodate this, it's extremely bogus.

    "Just hooking a ground wire to a cold water pipe" isn't right either. You can run a ground back to the main house grounding system. Installing random ground rods and just connecting them to the water piping isn't right either.

    Perhaps you should find a reputable electrician.

  • 19 years ago

    In Canada you can use the cold water pipe as an accepted ground as long as there is a copper jumper between the street and house side of the water meter. So what you did is fine as long as there is that jumper at the water meter. The new ground electrodes should be connected to the neutral/ground bar of the main panel. For 200A service we use #3 copper and for 100A service we use #6.

  • 19 years ago

    It would be permissible to run the conductor (#6 is usually OK) from the ground rods to the first 5 feet of the water pipe if the water pipe is, in fact, a grounding electrode. My personal preference is to bring all grounding electrode conductors to the service disconnect enclosure and make the connetion to the neutral bus.

    Maybe someday, it will be required that the manufacturers of GFI's also supply a small label that states "no equipment ground." Even the smallest labels I can make look unsightly. Of course, this added label would just confuse most DIYer's and some electricians too.

  • 19 years ago

    The Leviton GFI's I've been using came with 6 stickers each...

  • 19 years ago

    While a GFCI receptacle does not require a ground to operate corectly (it checks the hot current against the neutral current) any type of surge supression will provde limited protection without a ground.
    If you have expensive electronics it should be on a properly grounded circuit with surge protectors.