two appliances on 14-3 ?

20 years ago

i need to run new wiring to my garage to handle a side by side fridg and an upright freezer. the amps are 6.0 and 6.5.they are going to be side by side. i was told i could run 14-3 to a double box with two recepticals split the hots and pigtail the commons and connect to the main with two 15 amp breakers on seperate legs. anyone have any input on this? need to start this project right away.

Comments (14)

  • 20 years ago

    It is called a multiwire circuit.
    If you are experienced they are a snap.
    If you are not they can be confusing.
    You are installing a circuit that uses both legs of the 120 V in the main panel. That means there is 240 V betweenthe two hots. If there is NOT 240 V between the hots the neutral can be overloaded.
    Since both receps will be on a single strap the two breakers must have their handles tied together.

  • 20 years ago

    the trouble is that i only have 1 slot open in my panel. i also need to run a circuit for a disposal soon. i was going to use 4 skinny 15 amp breakers ,two would replace 1 indiviual on the full side allowing one hot space for the new garage circuit,the other 2 on the opposite side for the other hot and the disposal. how does this sound?

  • 20 years ago

    If the multiwire circuit feeds devices that are on the same yoke, they must be connected to a double pole breaker or handle-tied breakers. Even if not, it's safer that way.

  • 20 years ago

    If you are using the skinny breakers you wil have a problem with a legal multiwire if you use a duplex receptacel and split it.
    What you can do is install a two gang box with seperate receptacles (either 2 single or a pair of duplex) and then put one strap on each leg of the multiwire.
    For refrgerators and freezers I would use two singles to prevent any other device from being on the circuit.
    It is safer to have a multiwire on a handle tied pair of breakers, but it is only required if both legs feed a single strap.
    Neutrals must be pigtailed in multiwire circuits, no using a device (typically a duplex receptacle) to make a connection.
    Make sure you have 240 V betweenthe legs of the multiwire.
    In most boxes if you place the two 1/2 size devices beside each other they will be on opposite legs, but some older boxes do not alternate every slot.

  • 20 years ago

    if your amperages are accurate, 6 plus 6.5 is under the 15A limit of the 14ga neut. should work but i kinda think a frige and a feezer would use more amperage than that. w/o a circuit breaker to protect the neut, i would definitely find a way to plug in both and get an accurate amp reading before putting both on the same phase.

  • 20 years ago

    If the OP runs the freezer and 'fridge on a multiwire circuit, the neutral would only carry 0.5A given the operating amperage stated.

  • 20 years ago

    Why not do a single dedicated 20 amp circuit? 80% of 20 amps is 16 amps and only 12.5 is needed for the 2 appliances. Then you would only need one breaker.

  • 20 years ago

    Thanks for the input everyone! The 20 amp single circuit was my first though, but i was told than if both fridg & freezer motors start at the same time they may pull more current. That makes sense to me. the amps are stated on mfg labels in the units. the fridg is an energy star appliance. I meant to say in my original post "a double box with two duplex receptacles" the common ran to each & pigtailed together. Brickeye, If i put 2 skinny's in a single space in the panel [side by side], would they not be on the same bar or leg of the panel? Do i need to use two single spaces,[for the four skinny breakers]on the same side of the panel or across from each other to be in opposite phase from each other? This is where i'm confused!!! service panel is GE about 6 yrs old

  • 20 years ago

    Still fine with the starting, I believe they peak for only a few seconds. A breaker takes a while to trip from an overload. One house I was at with my ammeter clamped around a branch circuit, when flipping the breaker on starting the refrigerator it would peak up to 23 amps for 1 second and down to 6, the one second does nothing to the breaker and is safe. I have seen people with 2 refrigerators in the garage of a 1950's house plugged into a general lighting circuit without a problem.

    But if you do the multiwire ciruit, yes you can replace two double pole breakers with tandem breakers and where the single breaker was before would be one leg, and where the one below it was, would be a different leg. So just put red to one of the top two and black to one of the bottom two. However you may consider extending it to other gfci receptacles in the garage since there would still be a lot of room left on the circuit. Single reptacles would be good also for keeping the gfci requirement away which could be a nightmare for a freezer.

  • 20 years ago

    The 20 amp cicurit would be easier and cheaper to do if it will be up to code and SAFE.The only reason for the two duplex receptacles in a two gang work box is that i can't find a cover with two single openings!! is there such a beast????? I do allready have a gfci outlet in the garage [the only one outlet in a two car garage!!] but it is in the wrong place and is only 15 amp, or i would have removed the gfci and just extended the circuit to the new spot..

  • 20 years ago

    i can't find a cover with two single openings!! is there such a beast?

    If not, there are snap-together multigang plates, but they're costly and not all that attractive.

    You could make one. Get a plastic double switch plate and a single receptacle plate. Screw the receptacle plate to the switch plate, and carefully use it as a guide for your holesaw. Repeat on the other side. Now you have a 2-gang plate for two simplex recepts.

  • 20 years ago

    Ask your local electrical for one of these.

    Here is a link that might be useful: single receptacle wall plates

  • 20 years ago

    One reason to put these applinaces on dedicated circuits is that they may not be used on a daily basis.
    Few things are worse than going to a refrigerator or freezer and finding the power has been dead for the past week.
    I commonly try to wire a light used on a daily basis onto the same circuit so that any fauilufe is noted right away.
    While this does oncreas the slight chance of the light causing a trip, if you limit it to a singel 60 W bulb in a hall that is used on a daily basis you should be in pretty good shape to catch a trip before things become a problem.

  • 20 years ago

    Some places, like BC for instance, codes specify a dedicated circuit for a fridge and I"d presume a freezer, in the former code does allow an outlet for a clock. I suppose that's a way of checking power's available.