Old wiring mystery

17 years ago

I'm doing some renovation, and have a wall apart, and exposed the back of a simple 2-way switch with some K&T wiring going into it. No big deal, I think - I'll just replace as much old wiring as I can while I can get to it. (The front of the switch, and the chandelier it controls is in a room which is NOT being dismantled).

So, into the switch run 3 knob and tube conductors which all disappear into the ceiling above. I do a bit of testing before removing anything. Here's what I observed, with all 3 wires disconnected from each other, and the switch removed:

-After turning the circuit back on, all the other fixtures on the circuit still work fine.

-The bulbs on the chandelier are in.

-The chandelier that is controlled by the switch has voltage running to it! (tested using a pocket tester, the kind you hold near a wire or fixture).

-Wire #1 into the switch shows 120V when tested with a multimeter, with the other prong held to a known neutral

-Wire #2 into the switch shows about 15V when testing with a multimeter, with the other prong held to a known neutral

-Wire #3 shows no current, but shows connectivity with neutral

-When Wire #1 is jumpered to Wire #2, the light comes on.

So - my question, how should I wire this up before I cover the wall. I have easy access to hot and neutral from another circuit, if needed. If you have any thoughts, (other than "call an electrician"), or insight into the mystery, I'd appreciated hearing them.

Thanks

Comments (3)

  • 17 years ago

    Continuity measurements through the switch (in each position) would help. Which wires did it connect in the up position and in the down position?

    The hot indication at the light indicates the hot probably goes there first, and the neutral to the light is switched. That would account for the hot wire number 1. It would be a pain, but if you pulled all the bulbs out of the chandelier that might change the reading on wire number 1, confirming this guess.

    This is not considered correct now. For a ceiling fixture, it isn't a huge problem because you aren't likely to touch the hot and a ground at the same time, but it is a small risk. I would not tinker with this circuit at all until you are ready to totally rewire that light.

    The 15 volts would usually indicate a wire that is not connected to hot, neutral, or a load. Maybe to a switch that is OFF. It is a "phantom" reading caused by stray coupling to another nearby hot wire somewhere. Your meter does not represent any load to speak of, but a load would make it go away.

    I haven't figured out how connecting to wire 2 could make the light come on. Unless you lost track of your wire numbers during the testing, it is indeed a mystery to me.

    Is there another 3-wire switch somewhere in that room? I suspect that if so, flipping that switch would reverse the roles of two of your numbered wires.

    I wouldn't be surprised to find it was one of those old-style, now banned, arrangements where the light is wired between the common terminals of each switch, and the switches each connect to either hot or neutral. It saved wire in some cases, but the shell of the lamp socket may sometimes be connected to hot, which is not allowed now.

  • 17 years ago

    Responses:

    I'll try pulling the bulbs out and see what happens - if that does indeed cause wire 1 to go dead, I'll still be a bit confused about how the switch could have been connected to both hot and neutral, which is what seems to be the case here.

    Sorry - I misspoke - wire number 1 touched to number 3, not 2, makes the light come on. That probably makes more sense.

    There is not another 3 wire switch in the same room, but there other switches on the same circuit.

  • 17 years ago

    You should leave it alone until you can rewire the entire circuit.