Does this look like a ceiling fan-rated electrical box?

11 years ago
last modified: 11 years ago

My husband and I bought a foreclosed home (built in 2001) and are in the process of installing light fixtures (previous homeowners removed all of them). I'd like a ceiling fan in the master bedroom and am not sure if this is a ceiling fan-rated electrical box. They painted the metal box so there's no visible sticker/engraving stating that it is.
I can see two large screws in the middle of the box, presumably attaching the box to a joist. It looks like it also had some sort of "cross-piece" that they removed when they took the light fixture (or maybe it was a ceiling fan, too?). There aren't the "poles" for the screws, but there are double sets of "ears."


There are also 4 light switches on the wall (2 of which control can lights), so I am wondering if the other 2 maybe were for the light/fan of this ceiling fixture.


Any insight would be greatly appreciated!

Comments (7)

  • 11 years ago

    I think that having a ceiling fan-rated box is only a requirement for fans over 35 pounds...which is a very heavy fan and likely to be more than you will install. Your main concern should simply be how well that standard box is attached to the joist. Those could be short screws, and you won't know until you remove them and perhaps replace them with something longer (and, if you do that, use wood screws, not sheetrock screws).


    smiles33 thanked kudzu9
  • 11 years ago

    It does look like a fan-rated box (though it's ahrd to tell with all that paint in it. The telling part is that there apears to be more meat for the mounting screws to go through beyond the simple box tabs. It looks like it is well mounted to something with the two pan-headed phillips in the back of the box (I've never seen pan-headed drywall screws).


    smiles33 thanked Ron Natalie
  • 11 years ago
    last modified: 11 years ago

    Thank you both! I crawled up into the attic space and see that this box is mounted to a 2x4 in-between the joists. So that should make it pretty secure for a 22 pound fan (right?).

    I'm also looking for confirmation that the guess that they may have had a ceiling fan here because it has black, white, copper, and red wires. Is it true that you usually just have black, white, and copper (ground) wires? Or am I wrong to assume that the red wire is for a ceiling fan?

  • 11 years ago


    Smiles-
    As long as the 2X4 is well secured to the joists, you're good. There was probably a fan there before. The red and black should be hot wires and one can be used to provide power to the fan and the other to the light.

    (Ron- I wasn't suggesting those were pan-headed drywall screws. I was just saying that, if they were short, they should be replaced, and not with drywall screws, which many folks use as multi-purpose screws.)


    smiles33 thanked kudzu9
  • 11 years ago

    The red is for wiring the fan and ceiling light on separate switches if you want that. Otherwise it is usually a traveler for a 3 way switch (but there would need to be two separate lines entering the box for that set-up). Cap off the red on both ends if you aren't doing separate switches.


  • 11 years ago
    last modified: 11 years ago

    All ceiling fans, regardless of weight, must have a box listed for the use if the fan is supported by the box. It is more a matter of the vibration and wobbling that could strip the threads eventually. There may not have been a paddle fan there, but just wired for one as the second part of the code requires the listed box anyway. The code back in 2001 didn't include the second part, but it was still considered common sense and every electrician I knew back then did it this way.

    NEC

    314.27

    (C) Boxes at Ceiling-Suspended (Paddle) Fan Outlets

    Outlet boxes or outlet box systems used as the sole support of a ceiling-suspended (paddle) fan shall be listed, shall be marked by their manufacturer as suitable for this purpose, and shall not support ceiling-suspended (paddle) fans that weigh more than 32 kg (70 lb). For outlet boxes or outlet box systems designed to support ceiling-suspended (paddle) fans that weigh more than 16 kg (35 lb), the required marking shall include the maximum weight to be supported.

    Where spare, separately switched, ungrounded conductors are provided to a ceiling mounted outlet box, in a location acceptable for a ceiling-suspended (paddle) fan in single or multi-family dwellings, the outlet box or outlet box system shall be listed for sole support of a ceiling-suspended (paddle) fan.