Need advice: Solar AC Connection

10 years ago

The solar system we are planning will have 56 Amp AC output from four enphase branches. All branches are combined in a solar-only subpanel (rated 125 Amp). Branch OCPD are: 3 x 20 Amp , 1 x 15 Amp. Actual max total current output is 56 Amp.

Main electrical panel is a 400Amp panel, but it has two 200Amp disconnects. One of them directly goes to the home subpanel, the other one goes to an internal busbar rated 200 Amp. From there, it goes to the garage subpanel (225 Amp busbar, 200 main breaker).

This is the main panel:

http://www.homedepot.com/p/Square-D-Homeline-400-Amp-30-Space-40-Circuit-Main-Breaker-Outdoor-Combo-Surface-Mount-CSED-SU3040D400CB/100140344

This is the garage subpanel:

http://www.homedepot.com/p/Square-D-QO-225-Amp-54-Space-54-Circuit-Indoor-Main-Lug-Plug-On-Neutral-Load-Center-with-Ground-Bar-QO154L225PG/204246796

This is the solar-only subpanel we will use:

http://www.homedepot.com/p/Square-D-QO-125-Amp-12-Space-24-Circuit-Outdoor-Main-Lug-Load-Center-with-Ground-Bar-QO11224L125GRB/100192088


I have two options as to where I can connect the solar-only panel output:

(Option-1) To the garage subpanel:

225 Amp busbar, 200 Amp main breaker => 225 * 1.2 - 200 = 70 Amp

So, maximum 70 Amp can be backfed into this subpanel.

56 Amp * 1.25 = 70 Amp (looks OK)

This 70 Amp will go back to the main panel through the 200 Amp busbar of that main panel. I think this is OK, since there are 200 Amp breakers on the way before it can reach that busbar. So, main panel busbar cannot get more than 200 Amp. Is this a correct way of thinking?


(option-2) To the main panel:

I cannot backfeed main panel busbar, since it is rated only 200 Amp. But the only breaker on that busbar is the 200 Amp quad breaker feeding the garage subpanel. (I had to use that option, because I could not find a feed-thru lug).

Another option is to do a line-side tap using two of these:

http://www.amazon.com/NSI-Industries-IPCS4020-Insulation-Connector/dp/B00CUNJGU0/ref=sr_1_1?s=industrial&ie=UTF8&qid=1458285879&sr=1-1&keywords=Tap+Insulation+Piercing+Connector


I would rather use Option-1. Do you see any problem with that?

What would you recommend?


Guts of the main panel looked like this before adding connections to garage and house subpanels. I can add its current picture if needed.







Comments (2)