clint4590

Gate opener

9 years ago

I purchased a single swing gate opener that states, " this gate opener must be attached to a 10 amp circuit breaker"

i currently only have 20qmp breakers in my panel. I'd like to not hard wire it directly to the panel. I'd prefer to wire it on a 3 prong plug so I can unplug it as opposed to going to the service panel and flipping the breaker.

so my question is as follows. Can I connect the motor via a plug that is 20 amps.

Comments (8)

  • 9 years ago

    Standard dual receptacles for the home are rated for either 15 amps or 20 amps, and either type can be used on a 20 amp circuit because the plug design limits the 15 amp receptacle to 15 amp (max) devices. If the directions for your opener allow you to add a plug on its power feed, it should be acceptable to plug it into a 15 amp receptacle. However, sometimes the UL approval will require it to be hardwired.

    Bruce

  • 9 years ago

    There's two issues that I see here:

    (1) Can it be put on a 20amp circuit

    (2) Can it be changed to a plug instead of hardwired.

    Normally, the instructions that come with the unit trumps everything else.

    So if it states that it MUST be protected by a 10 amp circuit breaker, then it can't be installed on a 15 or 20 amp one. The thing that confuses me though is that 10 amp circuit breakers are pretty abnormal. 15 is usually the smallest. So I find this requirement weird.

    Regarding (2), Bruce covered that. The unit (hopefully) has UL approval and that approval may be just for hardwiring. It may also be for converting it to a cord, but if so, it probably mentions it in the instructions.

    Is this a known brand or some illegal Chinese import? Post the make and model and maybe we could see if we can find some information about it.

  • 9 years ago

    If the question is "will it work if I do these two things" then yes. But it may not be safe or to code.

  • 9 years ago

    Wondering why they designed that motor to fry at above 10 amps. Perhaps lowers mfg costs. Can we get the model number?

  • PRO
    9 years ago
    Here is a picture of the opener and the wiring diagram. But, I've already added a cord with a 3 prong plug into a 15 amp plug and it's working fine.
  • PRO
    9 years ago
    It's opening this gate fine.
  • PRO
    9 years ago
    Vith. It can lock from the inside. However with the motor on it now it will not budge unless you open it with the clicker. And yes due to codes etc I would have had to build a garage. That's why I went and purchased a welder ( never welded before) and watched a few welding videos then built the gate. The entire cost with the miller welder and to build he gate with motor was $2000. The most expensive part of the gate is the ironwood which is 1x6x10' and out here In Los Angeles runs $4.45 a foot. But it works great. Fuse has not blown yet.