Transition from old work box to conduit

9 years ago

How do I do this correctly? Photos show existing situation, which was done before I bought the house. It seems like the tie-in to the old work fixture box was done incorrectly given the exposed romex between the fixture and the conduit.


If that's true, how do I make the tie-in legal?


Ultimately, I want to add another 14/3 romex (15 amp circuit confirmed) up to where the existing conduit ends and put in an "always on" receptacle. Do I just mount a surface-mount box? The hot wire is at the switch, which is on the other side of the wall and just 2 feet below the fixture, so it should be easy tying in a new line for the receptacle.


Downstream of the proposed receptacle J-box, can I just get rid of the expose romex and run armored 14/3 to the black canopy overhead fixture?


Thanks,

Rileyann

Northern California


Comments (6)

  • 9 years ago
    last modified: 9 years ago

    Conduit L body which terminates inside the wall, then take the wire to the old work box body. They also have PVC type but you have metal so would need metal L body with the retaining screw. You can remove the screw for the part that goes in the wall.

    You will have to pull or push the wire back into the conduit a specific distance, cut the conduit, drill the hole in the wall, then install the L body, then pull the wire back through. You open the body up so you can make the wire turn the corner, then close it again once your happy with it.

    Since its exterior work, you would caulk around the conduit wall penetration.

    rileyann thanked Vith
  • 9 years ago

    Thanks y'all. Since I like to make more work for myself, I'm thinking of tearing out the metal conduit and using PVC rather than trying to tie-in to the metal. Plus I'd like to get rid of a hack job's work. Can I do that per code? I want to make it look nice so I'll drill a hole in my house, use the L body, and run the NM into the the existing j-box. What size conduit do I use if I want to run two 14-2 NM in it?

    For the proposed receptacle, I assume I'll want to use a plastic j-box if I can use PVC conduit. Are there particular surface-mount boxes to look for or will any of those old work blue boxes they sell at home depot work?

    Thanks again!

  • 9 years ago

    The biggest issue I see at the end of that conduit is the lack of a bushing or other fitting to allow the cable to exit the conduit (NM in most places is OK exposed, subject to some other concerns). I learned the hard way 25+ years ago that if you cheat on NM cabling passing over sharp metal edges, you're going to end up electrifying something.

  • 9 years ago
    last modified: 9 years ago

    Yea a bushing on a metal edge is always required when a stress relief isnt used. For either knock outs or end of a conduit. I prefer the snap in kinds.

    I would say 3/4" on the conduit. Should allow you to pull it through and guarantee allowance for heat dissipation.

  • 9 years ago

    I didn't see any 2-gang PVC boxes at Home Depot, so I did some online research and it looks like it's legal to use a metal j-box with PVC conduit. The location I plan to put the box is under a roofed patio and sheltered from rain. What am I overlooking?

    Thanks,

    Riley