insulation recommendation - attic

9 years ago

I'm looking to put in some insulation in my attic. What I have currently is R-9 batts, looks pretty old, and only about 3 or 4 inches deep. I need to get to about R-40, and am looking to get some unfaced rolls to put over top of the old stuff. My question is, though:

Should I roll it directly on top of the old stuff, between the joists? Or crosswise, perpendicular to the joists? The issue is that the current stuff is not up to the top of the joists, but several inches short. Is it still ok to put it perpendicular, leaving a few inches between the layers? Or should I lay it in the same direction as the old stuff and have the new stuff sit several inches over top of the joists?

Thanks!

Ethan

Comments (11)

  • 9 years ago

    About many inches is the old insulation below the top of the joists?

    Ethan Lennox thanked mike_home
  • 9 years ago

    If you can add a 3.5" unfaced bat on top of the old bat without compressing it, do that before putting the next layer perpendicular. An air pocket isn't awful, provided there are no leaks, but that is almost impossible to achieve.

    Ethan Lennox thanked sktn77a
  • 9 years ago

    mike_home, the gap varies but ranges from 2-4 inches.

  • 9 years ago
    last modified: 9 years ago

    My thinking is a 2-4 inch air gap is going to allow a lot of cold and hot air to bypass the added layer of insulation. The R value is not going to be as high as what is listed on the insulation material. I think you are better off laying the new batts parallel to the old ones.

    Ethan Lennox thanked mike_home
  • 9 years ago

    I would start with something like R-19 3" unfaced rolls on top of the existing to fill in the voids. Then I would use something like R-25 bats perpendicular.

    Ethan Lennox thanked weedmeister
  • 9 years ago

    Yes go parallel with existing insulation to fill the joist spaces, then perpendicular on top of that.

    Ethan Lennox thanked Vith
  • 9 years ago

    Thanks, everyone, for your advice. I ended up using R-15 3.5" unfaced batts, placed on top of and parallel to the existing stuff, which brought the insulation up above the joists. I then laid out R-30 9" unfaced rolls perpendicular to the joists. I think it turned out ok. Certainly one of the more annoying jobs I've done, but I think I've done myself a favor in the long run. Thanks again for your help!!

  • 9 years ago

    I was going to suggest this but did not since it is a lot of work. Glad to hear it worked out for you.

    Ethan Lennox thanked mike_home
  • 9 years ago

    For sure not fun, one of the few jobs better done in winter lol.

  • PRO
    9 years ago

    Do an internet search on Air Sealing first before you add the insulation. At that point, you can just loose fill blow over the top.