randy427

Switching from R-22

8 years ago

Is R-410A the best alternative to R-22? My church has 7 compressors, totaling 17 tons of A/C. They are about 20 years old and seem to be nearing the end of their useful lives. We are hearing that the 'newer' R-410A may be obsolete in about 10 to 15 years, and with the cost of changing out the equipment, we aren't eager for a 'short term' fix. FWIW, we have a well-sourced geo-thermal system that also provides our heat.

thnx, R3

Comments (7)

  • 8 years ago

    If church is having a gradual replacement program, I think phasing in R-410 systems is the way to go. I assume these are conventional split systems, AC only or HPs? discuss refrigerant selection and options with a qualified dealer.

  • 8 years ago

    If a geothermal system already exists, have you considered adapting if for cooling? I think it would be cheaper than replacing 7 condensers.

    The reason R-410A might be phased out in the future is because it has a high global warming potential (1700 times higher than CO2). It remains to be seen if someone can develop a refrigerant which has a lower potential. I don't think you need to worry about R-410A going obsolete in 10-15 years.

  • 8 years ago

    I would encourage you to maintain and continue to use the geothermal system – especially if it’s R22. These systems are very efficient and robust. Can you provide details of the geothermal system, particularly the bore field or wells?

    Expanding the geothermal system might be the best solution going forward for heating, cooling & Domestic Hot Water.

    IMPO

    SR

  • 8 years ago

    To clarify, we have heat pumps which provide both heating and cooling and use the water from about three dozen closed-loop wells for heat sink/heat source. We've no intention of abandoning the geo-thermal design. Since switching from R-22 will require complete system replacement, our quandary is whether to do it now or look and/orwait for something better than R-410A.

  • 8 years ago

    What makes you believe that they are at the end of their life-cycle?

    If they are serviceable, I'd use them and extend their life.

    You could replace those units that would not pay to repair with R410A units. The Entering & Leaving water from the boreholes have no bearing on type of refrigerant used. You should be able to 'mix & match'.


    IMPO


    SR

  • 8 years ago

    As you have multiple units, you can replace them individually if and when they die on you. You heard wrong on the life expectancy of R410a!

    randy427 thanked sktn77a