An Average Fridge needs 2200 Starting watts, and 700 Running watts.

When that Fridge is plugged in and operating normally,

does it "rest" for a while (when the door is not opened for many hours)

and then "restart", Thus Needing the Starting 2200 watts to "restart"?

OR, after initially Starting, does it always need just the Running 700 W?

Comments (6)

  • 4 years ago

    Well, Thanks for the reply, Rwiegand, but...

    OK, the BIG draw (compressor) cycles On and Off.

    WHEN it Cycles ON, does it... at that moment...

    take the 2200 watts to "restart"?

    I'm thinkin'... Yes? So therefore...

    That 2200 W Draw could happen at any time of the day.?

  • 4 years ago

    The extra current is pulled momentarily (less than a second) each time the compressor cycles on.

  • 4 years ago

    If this is a preamble to questioning the circuit rating, or breaker rating, please look up the trip current-time curve of typical breakers of the type in your panel and see how much time a 15A (1800W) breaker can operate at 2200W (18.3A). It is probably longer than a second. In any case, refrigeration devices should list a requirement for the size of breaker to be used. As for the circuit, which should be limited to the refrigerator, 15A should be fine from a thermal point of view, or you can wire for 20A to be sure of keeping the impedance down for the motor starting. For comparison, my 4 ft-wide SZ 632 refrigerator/freezer has two compressors, and it operates on a 15A breaker. A smaller Amana refrigerator/freezer from the distant past is operating in my basement on a 20A breaker, but I no longer recall the particulars. Dedicated motor circuits are usually allowed breakers suitable for the starting currents required. Refer to NFPA 70 for details.

    Mark thanked kaseki
  • 4 years ago

    EXACTLY, Dadoes! And the circuit breaker is apparently designed

    to Take that Momentary Overload. ? !


    Kaseki,... You are The BOSS!

    Well, you sound like it, anyway.

    The scenario is, actually, power requirements

    for when SHTF / the power grid goes down.

    I've got a Husky HU50011 generator...

    6250 Watts Starting/5000 W Running, 41.6 Amps for 120 VAC.

    I only really Need to run the garage Freezer and house Fridge.

    Anything else could be a bonus, and needs Few amps / watts.

    (Like microwave, flat TV, computer, etc...)

    I was wondering if my generator could handle it.

    I think the answer is Yes.

    Thanks very much for the lessons, people.


  • 4 years ago

    Thanks. I've been led to believe that analyzing generators is complex when the goal is to determine what the maximum transient current is that they can supply. It requires detailed knowledge of the generator magnetics, along with the rotational inertia of the drive. Less extreme conditions cease to be undetermined once the peak currents, added together, don't exceed the running current, in your case 41.6A, less whatever you added on for convenience of modern living. For continuous operation, generators are specified to 80% of peak capability (just like house service), and you will notice that 5000 = 0.8 x 6250. Likely your peak compressor motor currents plus extras could reach 52A without causing difficulty for the generator. (Frequency might briefly sag a bit.) How much more of a current transient might be possible is an unknown, and shouldn't be explored without being willing to sacrifice some hardware.

    Mark thanked kaseki