Why is my AC hardly cooling and not dehumidifying?

4 years ago
last modified: 4 years ago

Our AC is having some problems. The difference in temperature from return to supply is only about 12-14 degrees, and the air coming out does not feel dehumidified. In fact, while we have our AC on, the hygrometer actually will show humidity increase slightly the longer it's left on. The temperature in the house also hardly drops, even when left on for an hour.

Example: on an 80 degree day with 50% humidity outside, trying to lower the indoor temp from 74 to 72 may take almost an hour, and during that time, the humidity in our house may increase from 67% to 70%.

Context:

  • Our house is about 1600 sq. ft, built in 1958
  • Furnace is located in the garage
  • Three return ducts located in the attic
  • The AC is a 2 ton unit, both it and the furnace were installed around 2016
  • Crawlspace has a dehumidifier running, with a moisture barrier laid out (no vapor barrier on block walls though)
  • Air filter was replaced last week
  • Condensate trap was fine and the condenser unit was cleaned last week
  • Also aware that our attic insulation is low at around R16 and we need to at least double that
  • We have a fireplace, and I'm now realizing I should check if the flue is closed

We are already aware of an uninsulated 8' of return duct in our attic (attic is a little too hot, but that's being addressed), and also aware that our blower fan needs cleaned as it's a bit dusty. However I am not convinced that either of these are the root of our problems.

We're going to have a second opinion/deeper inspection and diagnosis from another company since I don't believe the first did enough to diagnose other than pointing out the return duct is not insulated and speculated that all need replaced without any testing.

I'm suspecting the following as potential causes, would really appreciate some input on what might be wrong here:

  • Low on refrigerant / refrigerant leak
  • Air leaks in supply / return ducts
  • Something wrong with the evaporator coils (pic below, unsure if that looks right)
  • House is letting in outside air from somewhere when the AC is on for some reason (idk if that's possible?)

Thanks all, please let me know if I can provide any other information to help diagnose, this has been driving me crazy and I'm dead set on getting this fixed.



Comments (10)

  • 4 years ago

    A temperature split of 12-14 degrees is probably a low refrigerant problem. The humidity rising means the coil is not getting cold enough to create condensation and remove the humidity. This also suggest low refrigerant. It could be something else, but I highly doubt it is an uninsulated return duct or dusty blower motor problem.

    Any tech who does a diagnosis without connecting a set a gauges is wasting your time. When was the last time the AC got a preventative maintenance check? You need to find a competent and honest HVAC company who will diagnosis the problem properly.

    Josh C thanked mike_home
  • 4 years ago
    last modified: 4 years ago

    @mike_home We just bought the house a couple weeks ago, so we are quickly seeing the difference between contractors to trust and ones to not, and this one definitely was leaning the wrong way there. They did preventative maintenance last week on it, but obviously did not do much else. We're already looking into another company to inspect this.

  • PRO
    4 years ago

    Hi, Josh,

    Your temperature and relative humidity data confirm sensible cooling only. You probably have a combination of issues including inadequate cooling along with infiltration of humid outdoor air. You have identified a source of moisture input from the basement. A couple of questions:

    What is the relative humidity in the basement?

    Does your fireplace require continuous venting such as one with gas logs? If not, can you install rigid insulation to block any back drafting of air down the chimney?

    Was the duct work replaced in 2016 when the furnace and a/c were? Is there evidence of mastic or foil tape sealing joints in the ducts?

    Josh C thanked Charles Ross Homes
  • 4 years ago
    last modified: 4 years ago

    You need to take the supply and return air temperatures at the air handler to see if the system is cooling properly. If you get a higher differential this way then the problem is with the ductwork (leaks/insulation). If the differential is the same then either the system just isn't very efficient or it is low on refrigerant. If that's ice on the indoor coil then that suggests low refrigerant.

    For any given water content in the air, relative humidity increases when temperature decreases. So if the air is being too cooled quickly, that may explain why you feel the humidity is higher.

  • 4 years ago

    @Charles Ross Homes Just noticed I said basement in my post, I meant to say crawlspace.


    All good questions. I cannot answer the duct work replacement, that's unknown to us. The ducts in the attic that I've seen so far do not have any sealing joints evident, so probably a good idea to do that.


    I believe that the dehumidifier down there does display the relative humidity so I'll check on that next time I'm down there, but I think that it is significantly less humid in the crawlspace.


    Fireplace is not gas log, it's wood burning. Where exactly would the rigid insulation get installed in the fireplace? Do you mean by essentially covering up the main opening to the room with the insulation to seal that up when not in use?

  • 4 years ago
    last modified: 4 years ago

    Also, I don't think that the vents to the crawlspace around the outside of the house are sealed yet since installing the dehumidifier, should those be blocked off by Styrofoam? I've seen conflicting opinions on this.

  • 4 years ago

    Check for leakage of the supply vents in the garage. Any leak can draw humid air from the garage and into the house. It also means any carbon monoxide from the running car can also be pulled in. Make sure you have working fire and carbon monoxide detectors in the house.

    What is your location. An outdoor temperature of 80 degrees is not that hot. The real test is when the outdoor temperature is 95 degrees. The AC may run continuously and never reach 72 degrees.

  • 4 years ago

    @mike_home I'm in the Midwest. Oh yeah I have absolutely no faith that this AC will reach 72 on a 90+ degree day if it can't cool 74 to 72 on an 80 degree, low/mid humidity day, hence my concerns here.


    Will check on supply vent leaks, and planning to install detectors this weekend.

  • PRO
    4 years ago

    Hi, Josh,


    You shouldn't have any HVAC supplies in the garage; that would violate the mechanical code.


    Joints in duct work should be sealed with mastic or UL approved tape designed for that purpose.


    Your crawlspace can be a source of moisture that gets pulled into the your home by a combination of stack effect and an HVAC system operating at negative pressure due to inadequate return air flow (most do.) If you're running a dehumidifier and the crawlspace isn't a sealed, conditioned crawl space, then you're spending money to dehumidify the outside world. I recommend you convert the crawl space to a conditioned crawl. One of the principal sources of moisture is improper grading within the first 10 ft of your home; there should be 6 in. of fall in that distance. Storm water should be directed well away from the foundation.


    You should be able to fit a piece of rigid insulation to seal the fireplace throat (entrance to the fireplace flue)--not the opening of the fireplace into the room. I suggest you include a ribbon that hangs down in full view as a reminder of the need to remove it before lighting a fire in the fireplace. Make sure any fresh air intakes for combustion air are closed, too.