I had a question regarding a couple of torchiere lamps i bought at home depot which use a three way switch for a three way bulb - 50, 100 and 150. i plugged them into outlets controlled by lutron dimmers and even when they are full-on, they buzz. When you dim them, they buzz louder.

i have several other hanging fixtures controlled by these same type of dimmers and there is no noise at all. Is this a function of the lamp wiring or maybe the type of bulbs?

i don't want to use them if i keep getting the annoying buzzing.

Thanks for any advice.

Comments (10)

  • 18 years ago

    Buzzing (or as some say, filament sing) is indigenous to all SCR-based dimmers (which all home ones are). It's worst at the 50% brightness. Try either a better dimmer or different bulbs. The lamp wiring doesn't contribute to it, but the lamp itself may contribute accoustically to the vibration.

  • 18 years ago

    Heavy duty, or long life, bulbs will have less tendency to buzz.

    Perhaps it would be good to mention that it is a code violation to have outlets contolled by dimmers?

  • 18 years ago

    It sounds like you possibly have some bad dimmer switches. When they are full on they should not buzz. These dimmers as most are triac based not SCR as many people assume. A triac will conduct in both directions a SCR will only conduct in one. To use SCRs you need two, triacs you only need one and the triggering circuit is much simpler. The triac and SCR with similar ratings cost about the same. Also noted is that some lamps are more prone to buzzing then others. The buzz is caused by mechanical vibration of the filament. It is turned on and off 120 times a second for 60 cycle current (the triac is fired in both directions). If the triacs are not fired at zero voltage they add a shock to the filament and that makes them more prone to buzz. If you can find some that advertise '0' cross turn on try one of them.

  • 18 years ago

    I think it was Petey Racer who told me to just get the bulbs labelled "heavy duty" or "rough use". Those have better filaments. I followed Petey Racer's advice and my buzzing stopped. I don't often find those bulbs at HD, but my neighborhood hardware store has them, also Ace Hardware and Menard's.

    Gilshultz, I am not sure that the OP or anyone else with a similar problem would find your post helpful, as your post is confusingly written. Are you recommending the SCR or the triac? What is the OP supposed to do with your statement "to use SCRs you need two, triacs you only need one". What is your recommendation and fix for the OP? And you have not provided any sources or models or names for whichever are the replacement dimmers you are recommending.

  • 18 years ago

    ronnatalie answered the question fully in his post. Then jcw48 added that heavy duty bulbs would help. The question is now COMPLETELY answered. Along comes gil and adds nothing but electronic theory that doesn't help the OP one bit.
    Then he states "If the triacs are not fired at zero voltage they add a shock to the filament and that makes them more prone to buzz. If you can find some that advertise '0' cross turn on try one of them."

    The OP is not looking to buy triacs or dimmers. The OP is not looking for a lesson in electronic theory. The OP is looking to get rid of buzz. He was told how to. No need for rehashing something that has already been fully addressed. Again, posting for the sake of seeing your own posts sure doesn't help anybody on this forum.

  • 18 years ago

    Yes GilShitz I know what an SCR and a TRIAC is and how it works. I have worked with just about every dimming technology (with the exception of a thyratron, but I did have one sitting on the desk as a curio). I've done theater/special events lighting with resistance dimmers, autotransformers, magnetic amplifiers, and a wide range semiconductor dimmers. I've repaired and restored each.

    If you're trying to build a dimmer, you can't fire it at the zero crossing. A SCR/TRIAC once fired conducts continuously until the voltage drops to zero. To dim, you must fire somewhere between the zero crossings. A zero-crossing device is great if you're building a dumb switch but it won't work here.

  • 18 years ago

    Good observation, at zero crossing they will be just a switch with maybe about a 2V drop depending on the unit.

    You work with I designed them. For optimum noise reduction etc the best place to turn them on is just after the voltage passes zero. In the electronics world that is exactly what zero crossing means. Check with Motorola and others, start with a Fairchild app note AN-3004, you can get it at; http://www.fairchildsemi.com/an/AN/AN-3004.pdf.

    You might look a bit closer at my post, I stated; "If the triacs are not fired at zero voltage" which is exactly what a dimmer does; this is called phase control. At full on they should be firing at the zero crossing point. I did not say fire at zero crossing.

    A SCR conducts only in the forward direction, the Triac conducts in both directions and can be fired in one of four quadrants, and the SCR cannot consequently they use a triac not a SCR in lost cost dimmers. Lithonia and others use SCRs in commercial dimmers but they are configured in a back to back configuration on each phase so they can conduct in both directions. Also if you look at a data sheet for either device you will see a "holding current" specified. When the current falls below that the device shuts off until retriggered. Add an inductive load and the rules change.

    When it is full on it should be firing at zero crossing, a lot of the cheep ones do not. Trigger circuits and noise control for these devices can get very complicated.

  • 18 years ago

    OK Gil, but how in the hell does all this EE mumbo-jumbo help Harry Homeowner (no offense ptnr) with his buzzing lamp????

    At an electronics web site that might be very helpful and useful information. This is a DIY site. As in homeowners doing things themselves.
    Are you suggesting Mr. Homeowner build his own dimmer?

  • 18 years ago

    Simple, I explained the cause, I did not give nor intend that the typical person build one. If you understand the system you can understand the results. Change the filament configuration and the buzz will change, that is what was suggested but no reason given as to why. The solution given does not always work. It is more fun on 50 Hz systems and no buzz on 400 Hz systems.

    It also corrected a statement that home dimers are built with SCRs, they are not.

    Sorry you did not understand the response and conversely I did not know that this was just DIY postings, I assumed (wrongly)there were some professionals with some knowledge of what is going on and had an understanding of what they expouse.

  • 18 years ago

    There are LOTS of professionals here. Professional ELECTRICIANS, answering DIY questions.
    This is NOT an EE site. Maybe some of the electrical contractors here that have extensive engineering or electronics backgrounds will get what you are saying, but most of us "regular" electricians and DIYers (which is by far the majority on this site) find this information useless.