2 slot outlets

17 years ago

Recently renovated my bedroom and while the electrician was installing a new lighting fixture, he commented that my outlets are all out of date and should be replaced by grounded 3 prong ones. My question is this....what purpose does that serve when nothing I have in the bedroom such as lamps and clock radio have cords that have 3 prongs on them?

Comments (7)

  • 17 years ago

    The NEC does not require updating those receptacles so long as they are in good condition and meet the applicable code at time of installation. Some building codes use a backdoor approach by requiring that everything, including electrical, be updated to most recent code if damage repairs, additions, remodeling is undertaken that exceeds 50% of the value of the premises prior to any damage or rework.

  • 17 years ago

    It serves no purpose in your case since only have two prong devices.
    It could be a resale issue or at some time you may need to plug in a three prong cord and won't be able to.

  • 17 years ago

    you can not just simply pull out the old outlets and pop in a new shiny 3 prong one and call it good.
    If you don't have a ground wire in your boxes to hook up to the new devices putting in a 3 prong outlet is against code. You're only option if you don't have a ground wire in your boxes and you want a three prong receptacle is to install GFCI receptacles.

  • 17 years ago

    I would question an electrician suggesting grounded outlets if the circuits are not grounded. What you have on a circuit is immaterial. You need to understand the purpose and reason for a grounded system. Also, very few lamps, radios, vacuum cleaners, etc., have 3 prong plugs. The main reason for a grounded system is to prevent shock if one of the items should short out.

  • 17 years ago

    Thanks for all of your replies.
    I did some additional research in the meantime. Local code in my town does not permit plastic romex wiring or plastic boxes. Only steel boxes and steel bx cable are permitted which is what I have. Since the main panel box is grounded on the incoming cold water pipe, I was told the entire system is grounded and green ground wires are unnecessary but 3 slot outlets can be used. However, I checked around the entire house and outside of a few outlets they are all 2 slotted so I decided to leave them as they are.
    Thanks again for your help.

  • 17 years ago

    This is very easy to check. Pull the outlet cover off and place one of the probes of a circuit checker on the hot slot and the other on the side of the outlet box. If it lights up you have a ground.

  • 17 years ago

    The hendricus test can often be done by using the center screw on the outlet, even on the non-grounding (two-prong) variety.