service ground

19 years ago

located in canada: anyone have any important info or tips on service grounding with an electrode? i will be using a ground plate instead of 2 ground rods and the house does not have any metal water piping. 100 amp service.

also: master electrician tells me that the latest cec code requires 20 amp kitchen plugs, only my new code book states that it is optional (split 15 or just 20a). I do know it would be difficult to split a gfci plug...hahaha, but just looking to see if anyone has any input on this in canada.

Comments (4)

  • 19 years ago

    20 amp kitchen receptacles are optional except that receptacles within 1 meter of sink need GFCI. Not practical to GFCI 15amp split receptacles so use 20 amp for those. You can use 15 splits elsewhere if you like.

  • 19 years ago

    Use a standard size ground plate available at the big boxes. Make sure the lug and bolt for it is non-corrosive (SLU 70). It'll be brass or copper, not steel. I'm not sure of the burial depth in your jurisdiction. I've never installed a ground plate, only rods if I can't use the municipal water supply pipe. Ask your AHJ.

    Split 15A counter top recepts are still allowed, but not in the 1.5m zone around the sink. There you must use 20A GFCI recepts or a GFCI 20A breaker. No split 20A recepts. Only 2 recepts on each 20A cc't allowed. The old rule that adjacent recepts must be on different cc'ts is now gone, as only 2 recepts are allowed as just stated. There is a special provision in the code for disabled persons (26-710d). I won't get into the particulars as I've never done that and it's probably irrelevant to you.
    BTW.... the Oilers sucked this year, but you already knew that :-) Go Canucks!

  • 19 years ago

    ok, thanks for the reply's. Just wondering b.bird, why dont you use the plate instead of the 2 rods? I guess where i'm at the backfill has just gone in so the ground is quite easy to dig up(24" depth i believe in alberta). I am currently studying my masters and recently have been given the contract to 35 houses so i am having another master pull permits for me until i get mine. I've got plenty to learn yet in the res industry but it'll come especially with the reading material here. hopefully write and pass masters soon, getting tired of paying 1300 per house for this guy to inspect and pull permit...oh well.

  • 19 years ago

    Our soil is clay based where most of the population lives. Ground rods drive easily and are much cheaper than plates. Once you get into Pre-Cambrian Canadian Shield, there is the hardest rock in the world underlying a thin topsoil. That's where we'd use a plate.