suvdave

Mounting Sub-panel next to Main Panel - space requirements?

18 years ago

My main 200 amp service panel, which is directly mounted on a basement concrete wall 21" from one corner, is full. I need to add several new circuits for a basement shop and plan to add a sub-panel. The most convenient place for this is adjacent to the existing main panel between that panel and the corner (21" of wall space). I have no problem with the 36" of working space in front of this wall. My question is this:

Can I install the sub-panel in this preferred location and still satisfy 110.26 A(2) that requires the width of the working space to be at least 30"?

My interpretation of this is that you need to have an adequate area in which to stand and work when servicing the electrical panels. I have read one opinion online where it was interpreted as meaning each panel needed it's own 30" of wall space. Since the sub-panel is only 14" wide, I will still have at least 3" of space between it and the main panel as well as between it and the adjacent wall.

As an alternative, I could always mount the sub-panel on the adjacent wall, so that it's facing 90 degrees to the main panel. The 36 inches of working space depth required for each panel would then be overlapping. Would this be a better approach?

Also, my understanding is that I should use a 1/2 inch plywood backer board behind the sub-panel rather than mounting it directly onto the painted cement wall. Is this required or just good practice?

Thanks for any help,

Dave

Comments (7)

  • 18 years ago

    Dave, I think you're OK with that placement, but I suggest you confirm with your local building dept. The plywood is for insulation, and it's indeed a very good practice.

  • 18 years ago

    Insulation? Plywood isn't a particularly good thermal insulator nor is it tremendously useful electrically.

    The main reason for the plywood backing behind panels is to give a convenient place to secure the wires coming in (as well as mounting some ancillary things like doorbell transformers, etc..).

  • 18 years ago

    Have you considered replacing some of the standard sized breakers in the existing panel with the slim breakers that fit two breakers in the space required for one standard sized breaker? In my own panel I have 10 double breakers.

  • 18 years ago

    You also use shoddy wiring practises, Texasredhead. The OP has the right mindset to install a subpanel rather than add further circuits to his main panel.

  • 18 years ago

    If your panel is rated to accept the slim breakers there is nothing shoddy or wrong with using them.

  • 18 years ago

    Thanks for everyone's input. My main panel has 30 spaces and allows a maximum of 40 circuits. It already has the full complement of slimline breakers and is maxed out at 40 circuits by the builder. I'll need to move a few circuits over to the sub-panel to make room for the double pole 70 amp feeder breaker.

    By the way, the main panel is rated at 200 amps and I calculate my current home load at 87 amps, so I have plenty of capacity available for the 40 or so amps I intend to use from the sub-panel.

    Dave

  • 18 years ago

    Sounds like someone went circuit happy if you have 40 circuits and only use 87 amps. I think lonesparky answered your original question.