Open ground from sub panel - Really?

18 years ago

Preparing for the final electrical I plugged my circuit tester into a receptacle. It reads "open ground". I tried another receptacle in that circuit and it reads the same.

I test another circuit and it's the same.

Scenario - 200 amp main service with a 100 amp sub panel. Sub panel and four original circuits installed by licensed electrician (pulled permits). I added more circuits. All the circuits on the sub panel test bad.

All the circuits on the main panel test good.

I know the ground-neutral jumper is supposed to be disconnected in the sub panel. Is that the reason my circuits seem to fail? Some other special reason?

Panel includes 110 and 220 circuits, and one in-panel GFCI.

(Retested with my buddy's tester with same result)

Thanks.

Comments (4)

  • 18 years ago

    I know the ground-neutral jumper is supposed to be disconnected in the sub panel. Is that the reason my circuits seem to fail?

    Well, it is correct not to connect the neutral bar to the equipment ground bar in a subpanel so I can't in good conscience say that is the reason the equipment grounds test bad. Neutrals and equipment grounds are properly bonded in one place only--the main panel.

    I'd start out by inspecting the main-to-subpanel wiring. The normal case is that there are four wires running from main panel to subpanel (two hots, a neutral and a ground). The ground wire should be well-connected to the ground bar in the main panel on one end, and the subpanel's ground bar at the other end.

    Have you tested hot-to-ground in the subpanel?

    Above all, don't just jumper the ground and neutral bars in the subpanel. That would very likely make the problem appear to go away, but it isn't the correct solution.

  • 18 years ago

    Adding a question: Since you say you tested several circuits, did you test any circuit that was installed by the licensed electrician?

    If so, and that circuit did not come up with an open ground condition, the problem must be with your wiring rather than the wiring to the ground bar and we can walk you through diagnosing the problem.

  • 18 years ago

    There should be a GREEN (or BARE) wire running from the SUBPANEL equipment grounding bus to the main panel ground.
    Make sure that's hooked up (at both ends).

  • 18 years ago

    As I said in the original post, all the circuits in the sub panel test bad.

    I'll go open up the main panel this weekend and see. There must be something disconnected there.

    Thanks, for now.