chuckgiannone

Installing outlets - up or down

20 years ago

Is there a correct way to install outlets?

Our electrician has installed all our outlets with the grounding hole on the bottom. I thought the hole should be on the top. It feels natural to plug in a cord with the grounding plug on the top.

Or am I being to "anal".

Thanks,

Chuck G.

Comments (39)

  • 20 years ago

    I've traditionally installed them with the ground pin down (so they look like a little face). Most literature shows them this way, but it's a hotly contested item and there really isn't any predominate justification for one way or the other.

  • 20 years ago

    Not to put too fine a point on it but, the NEC does not address the issue.

    (either way is okay with the Code.)

  • 20 years ago

    This is PO-TAY-TOE/PO-TA-TOE issue.
    Code does not care, only the end userdoes.

    I will say, 90% of the electricians I know do ground down for reisdential and ground up for commercial.

  • 20 years ago

    >there really isn't any predominate justification for one way or the other.

    Well, except for when you're using a device with a digital display that "mounts" directly to the receptacle (e.g. a programmable electronic timer). Here, the assumption invariably seems to be "ground is down."

  • 20 years ago

    There seems to be regional preferences. I grew up on the east coast and the ground pin was always down. Now in Illinois for the most part, they're mounted side-ways. The ground pin can be left or right, that just seems to be the preference of the electrician.

    Mike

  • 20 years ago

    Yeah, but that's Illinois (rolls eyes).... ;-)

  • 20 years ago

    One thought I heard, (I didn't make this up), is that if the ground is down and the plug is pulled half-way out and something metallic falls and lands on the prongs, sparks'll fly. It was assumed metallic objects will be more likely to be flying around the room and fall rather than jump up from below.

    Seems like a stretch. I prefer the face, ground down.

  • 20 years ago

    I see mostly ground down. So many people say it's user-choice, but I really think it's 98% ground-down. Residential and commercial.

    Someone once mentioned a reasonable safety feature that if a plug was pulling out of the wall half-way, and someone was to drop say a fork near the wall, it would be safer to have the ground up so the fork doesn short the plug.

    That's the only safety thing I can think of, and it's an extremely rare / improbable situation.

    So I'd go ground-down, just to not have ppl look at them and wonder why they're backwards. Unless you like being different, then I'd do ground up! :)

  • 20 years ago

    Mullin's book (which many of today's electrician apprentices study out of) says ground hole on top.

    I, however, have a safety argument for ground down: you've all seen cords that are coming out of the receptacle. They always hang down slightly--thus the prongs on the top are further out than the prongs on the bottom. If the bottom prong is the ground, then the ground will be the last (rather than first) to disconnect, which is how you want it.

  • 20 years ago

    The ground pin is longer. It's "break last" feature shouldn't really depend on which way the receptacle is mounted. Further, the argument assumes that all stress on cables are gravity related. Actually, things that pull plugs untimely from the wall are just as likely to be sideways stretches of the cords.

  • 20 years ago

    Home appliance manufacturers seem to mostly turn thumbs down. The vast majority of right angle plugs will have the cord exiting at the bottom (as it should) when plugged into a ground-down recept. I've seen only one which exited upwards (designed for a ground-up recept).

    However, I have seen several plugs on which the cord exited at various angles (probably for easier use with ground-up recepts). For example, my computer UPS under the desk here has the cord exiting at 45 degrees to the right and downward when plugged into my ground-down receptacle.

    At any rate, I always mount ground-down. This is partly for the above reason, partly from habit, and partly because that's how the first grounded recepts I ever saw (in my grade school, 1960s) were mounted.

  • 20 years ago

    one local city here requires that the ground be up. other areas are all user preference.

    when i did my workshop i put the ground up, but only because i was not paying attention on teh first one and turned it that way when installing it. i decided to jsut do them all like that rather than go back and turn that one. lazy, sure, but i was working for free!

  • 20 years ago

    I prefer ground pin up. Once one of my daughters had a belt made of linked together metal circles, this fell across a two-prong plug and didnt throw the beaker right away. It melted the lamp plug before the breaker finally tripped. Luckily no fire. I am also gradually replacing non-GFCI circuits with AFCI breakers, except the refrig, and freezer dedicated circuits.

  • 20 years ago

    I prefer ground pin-up. When one or the other is specified, pin-up seems to be the installation specified, at least in my experience. However, for residential work, I almost always install a double duplex receptacle assembly with one duplex receptacle pin-up and the other duplex receptacle pin-down.

    I do this because the $#@ manufacturers seem to make about 50% of their appliance plugs pin-up and 50% pin-down. It just makes it easier for me and for the eventual home-owner. It does draw questions, though.

  • 20 years ago

    The data is compelling that they should be up, although the NFPA (writers of the NEC) refuse to accept it. They say because pre-wired cords can sometimes be oriented for ground down, then it becomes a user preference. I guess manufacturers are now dictating safety. What is ironic, is that years ago, the code required them to be up! I think that's why older electrician's probably still put them up and see the safety in it.

    With the ground prong up, the hot and neutral do not become exposed from the weight of the cord. Further support comes from the fact that ignitable materials, such as paper and fabric, could lay across the conductors and catch fire, when enough heat is generated through the cord. This is a real occurance, where doucmented bed fires have occured in hospitals, and people have been severly burned or died.

    I will always put mine up, and recommend to others to do the same. My families safety comes first and foremost. Besides, I think it looks better.

    Something to keep in mind. The one's indicating it should be on the bottom, are the same one's that will put as many outlets on as few circuits that the code allows. That doesn't make it practical, or user friendly. Remember that each time the breaker trips when you plug in your vaccuum cleaner, with the ceiling fan on.

  • 20 years ago

    hah ceiling fan with vaccuum cleaner. Reminds me of a old man's house I've helped vaccuum before. Turning the vaccuum on brings the chandalier down by 20%. Must be a loose connection in that wire job. Never tripped the 15 amp breaker though

  • 20 years ago

    that is the whole time the vaccuum is running too.

  • 20 years ago

    The one's indicating it should be on the bottom, are the same one's that will put as many outlets on as few circuits that the code allows.

    This seems like an odd parallel to draw. I install ground-down, but I certainly don't max out circuits, and I suspect there are many others here who could say the same thing.

    I hope you're not suggesting that because we install receptacles ground-down, we're somehow unethical, or are shoddy workmen. If the code mandated ground-up, of course that's what we'd do; but it doesn't.

    Personally, I'm not (yet) sold on the safety advantage of ground-up. If you're interested, my reasons for ground-down are discussed above. To that I would add that I think a plug with its cable exiting at the top is not only inconvenient; it may also be less safe because of the tripping hazard and the greater strain on the wire and connections.

  • 20 years ago

    I totally agree with David's comments. That statement was WAY out of line Bruce.

  • 20 years ago

    Don't know if it's local code... all the homes we have lived in are installed ground down EXCEPT the outlet operated by the wall switch which is ground up.

  • 20 years ago

    "The data is compelling that they should be up..."

    And just what data would that be?
    Got a citation to a study?
    You can claim all the reasons you want and cite all the anecdotal stories you want, I have yet to see any actual evidence that it matters.

  • 20 years ago

    I will always put mine up, and recommend to others to do the same. My families safety comes first and foremost. Besides, I think it looks better.

    It looks better?? Now who could argue with that sort of logic?

  • 20 years ago

    Ground up for me unless it's for a right angle 3 prong plug. If it's a wiring job, I always ask the customer their preference. When they invariably ask "what's the difference", I explain the safety aspect versus the 3 prong right angle plug aspect. They always choose the safety aspect.

  • 20 years ago

    There is a third option to ground up vs ground down: some ground up and some ground down. After reading Mullin's book suggesting ground up, I started putting new receptacles ground up. I had to agree with my wife that mixing them looked worse than either all ground up or all ground down. So I turned the new ones to ground down also.

  • 20 years ago

    Correct me if I'm wrong, but the specific purpose of the ground pin is to provide the ground connection for a 3 wire cable and the device(s) attached to it. I haven't seen any literature that extolls the advantages of placing the pin one way or the other published by a testing house.

    There are 2 schools of thought. Personally, if a plug is partly out and something metal falls on it I'd like the breaker to trip. If the slots are up the metal falls across the hot and neutral, which SHOULD trip the breaker. With the pin up you have a 50-50 chance of tripping the breaker.

    Personally, I put them down and turn them over when I find them the other way. I charge extra to mount the ground hole up simply because I don't think you should. The possible exception is switched receptacles but even there with the new labelers available I generally label the receptacle and mount ground down.

    All that said, I'd have been just as happy if the plugs had all the connections in a row so we could fuss about the big slot being on the left or right (left)

    UNK

  • 20 years ago

    Maybe we should suggest the manufacture of a duplex that has ground pins at both ends and the hot and neutral toward the center. Then there would always be a way to plug in the damn transformer plug with the cord coming down. And it'd be symmetrical. Cool.

  • 20 years ago

    For those of you who just can't decide ...

    Scroll down to page 7 and 8 and check out the triplex and sixplex.

    Here is a link that might be useful: up, down, sideways? How about all three?

  • 20 years ago

    "Scroll down to page 7 and 8 and check out the triplex and sixplex."

    Coolest receptacles I've ever seen!

  • 20 years ago

    Hmm, the way most right angle plugs are designed, with the cord exiting on the ground pin end, you could plug only ONE (or at most two) into this recept. The cord would block or partly block one or more other slots.

    Something else funny here. The brochure says "the industry's first triplex receptacle," but that's not so. I owned a home many years ago which had a triplex receptacle. It had an integrated cover (cover and recept molded as one piece) and screwed directly to the box. Strictly 2-pin, though; it had no ground pins. Wish I had a picture of it.

    That same 1920s vintage home also had a bunch of ancient duplex recepts of one-piece molded bakelite, again without a separate cover. The mounting screws had tiny threaded holes into which were screwed decorative ribbed covers! (Many of these covers had been lost over the years.) Regrettably, these recepts were all worn out, and I replaced them with modern duplex recepts. Again, I wish I had a picture, or had saved one.

  • 20 years ago

    David, what you had was Despard device. The triples were very common.
    The Acenti ad should have stated "The first grounded triplex receptacle".

  • 20 years ago

    I always do ground down. When I am doing wiring the ground tends to be the first wire I hook up. This is for a few reasons: First in the area where I work (and when I wire) the wires typically enter through the bottom of the box and the hook up for the ground wire is on the bottom of the recepatcle in this case. The next reason for ground first is so I dont forget it (things happen when in a hurry). Lastly I find it easier to hook up the ground then hook up the other wires rather than vice- versa.

  • 20 years ago

    what you had was Despard device.

    No, believe it or not, this one was NOT a Despard. It was all molded as one piece, cover and body, from ivory plastic. The was no separate metal retaining yoke, there were no snap-in devices. Very unusual. I've never seen another one like it.

  • 20 years ago

    Hmmm. Interesting.

  • 20 years ago

    I've pulled 3 outlet receptacles from a 1930's home, they were all one peice. However I think they may of been changed from the original receptacles so they may of been more like 1960's receptacles. The kitchen there was remodled in the 60's with grounded 12/2 and the receptacles were 3 outlets. Also had a plumber friend in Ohio that pulled out porcelain 3 outlet units from a cabin built in the 20's They mounted right to the baseboard and had openings for knob and tube lines.

  • 20 years ago

    Spencer, you're in about the right era. This one would probably have been installed in the late '50s. Sure wish I had a picture of it.

    I'd love to see those porcelain recepts! I think old wiring bits are interesting, especially the unusual or "luxury" items.

  • 19 years ago

    I am a Master Electrician in Virginia, and have been since the late 1980s. The NEC does not dictate whether the ground should be on the top or the bottom, and it never has, for a very good reason: it makes no difference from a safety standpoint. None. It's an urban myth that one way is safer than the other, and just like any other urban myth you'll find people steadfastly claiming it is so, but you won't find any verifiable evidence for it.

    Now, as a practical matter, the vast majority of manufacturers assume that the ground is on the bottom. For this reason, I install receptacles with the ground plug on the bottom. But that's a matter of preference and convenience, NOT safety.

  • 19 years ago

    I like what my electrician did for my new-house wiring. All outlets are ground-down, except for the switched outlets which are ground-up to distinguish them. Makes my life easier when looking for the switched outlets.

  • 16 years ago

    Ok just from a woman's point of view, I could care less about the direction of the ground plug, but nearly all the fragrance plugins come where the ground must be down or they are upside down and would leak out. I know from experience and I do like my fragrance plugins.

    Also like others when the ground is placed up, the cord on some appliances and other items goes up the wall and is unsightly.

  • 15 years ago

    OK people, go outside, drop a tennis ball (or ANYTHING) and where does it fall?? Down, to the Ground! Ground is down... DUH