Software
Houzz Logo Print
copelt

low voltage lights over the pool

18 years ago

I was reviewing NEC 680.22 and found that low voltage lights are not allowed within 10 ft of a pool. (Low-voltage lighting systems, such as those covered by Article 411, shall not be within 10 ft of a pool, spa or hot tub even if GFCI protected [411.4]. )

However , high voltage lights are allowed in some cases and can even be extended over the pool in some cases. Also, all my pool lights are themselves low voltage and they are in the walls of the pool. Can anyone explain why NEC forbids any low voltage lights within 10 feet of the pool without exception?

I have an umbrella with built in low voltage lights which extend out over the pool. Am I endangering those within the pool?

Comments (5)

  • 18 years ago

    Because any lights within 10 feet of the pool must be GFCI protected. You can't GFCI protect low voltage lights, even when you plug the transformer into a GFCI protected outlet you are only protecting the primary side.

  • 18 years ago

    thanks joefixit,

    I think you have explained the logic behind the code. Is this logic based on sound electrical science?

    Some cities forbid high voltage pool lights per local code. So I "presume" this means they believe low voltage pool lights are safer. The entry of water into a low voltage light without GFCI must be safer than water in a high voltage light with GFCI protection. Does anyone have an opinion on this?

    If these industry assertions are true then why is NEC apparently so concerned about low voltage lights mixing with pool water. I am not asking you to explain how NEC writers draw their conclusions (unless you happen to know) but instead I am asking how actual science applies to this discussion.

    Is NEC just refusing to make an exception to the GFCI rule or is there really a more significant threat involving low voltage lights than the pool industry would have us believe?

  • 18 years ago

    Wish I could help you there. I've never heard of anyone getting electrocuted by a low voltage light, but maybe it has happened. Could also just be over cautious on the part of the CMP.

  • 18 years ago

    Under the wrong circumstances even low voltage like 12 V can be deadly.
    The circumstances generally involve things that greatly lower the skins relatively high resistance.
    Water, and ions like salt that can aid conduction are the usual culprits, along with medical equipment that places conductors through the skin.

    Once you get past the skin, humans are relatively good conductors with a low resistance.
    All the salt and ions present do the trick.

  • 18 years ago

    Some common sence. What would make the lights deadly would be a failure of the transformer allowing 120v to go to the lights. The possibility of this is slim, but codes dont play the odds. The lighting transformers used in the pool have an isolated secondary with a grounded plate between the primary and secondary. basically it is designed so 120v can not get to the light.
    If you want to be safe you could install this type of transformer to feed your lights.