hillboy_z24

Replace or splice

18 years ago

I live in PA. I have a detatched garage which is located 20 feet from the house. I am looking to get power ran into it. Right now the person who built the garage had ran copper #6/2 wire through a 2" diameter orange conduit. THe problem is, they only ran it from the corner of the house that is closest to the garage, into the corner of the garage closest to the house, leaving about 6 feet of wire hanging out of each end of the conduit. The main panel in the house however is in the corner on the other end of the house.

I am trying to decide whether I should run #6 wire from the main panel to where the wire comes into the house from the garage, and just tie them together in a JB. Or if I should run all new wire.

I am trying to do this without spending alot of money. So I'd rather just splice the wires due to the cost of copper wire. That would involve running approximately 60'. But, I have also been told that the aluminum SER wire is half the price. So, I would be able to run all new wire out there, about 125', and plus step it up in size. I am planning on putting a sub-panel in the garage. I purchased a GE 100 amp breaker box, which came with 4 20A single pole breakers.

I am very mechanical, so I would like to be able to be able to have a welder, compressor, and anything else that I might like to buy later on without the fear of tripping the breaker.

What can I do so that I can get maximum Amps in the garage, without spending alot of money?

Is the SER wire my best option, or am I just better off tieing in the #6 and just putting in a 60A breaker?

Sorry for being so long winded, I just want to be able to give you as much detail as I can about my situation. BTW the main panel in the house is 200A.

Thank you in advance for any advice you can give me

Comments (10)

  • 18 years ago

    Using the existing 6/2 cable you won't be able to install a 120V/240V subpanel. You need 3 conductor cable, having 2 hots, neutral, and ground. You'll have to rewire to meet your needs.

  • 18 years ago

    Cable is not allowed in conduit except for short sections for physical protection.

    The insulation on the individual wires in underground conduit must also be rated for a wet location.

  • 18 years ago

    Sorry, hillboy, it doesn't look good for your existing 6/2. You need three conductors +gnd. Forget SER and SEU (approved only for above-ground use), and any other cable notions ye' might have.

    You know how it goes, sometimes ye' do more work avoiding work than the work would'a been in the first place. Git to trenchin'.

  • 18 years ago

    Thank you all for your knowledge.
    What should I run than to be able to install the 100 amp panel in the garage? I already have the conduit underground going from the house to the garage. I thought that the SER wire is made for wet locations

  • 18 years ago

    I would use #2USE AL, should be the cheapest way to go. You cant bury SER.

  • 18 years ago

    Could I just splice into the #6/2 that is currently ran out to the garage?
    Won't that only give me 120 volts though?
    If I were to run 6/3 I'd be able to get 240 volts, and won't that make the amp capacity double also?

  • 18 years ago

    With 6 gauge wire, you are limited to 55A, but you can protect the circuit with a 60A breaker since 55A is not an available size. You can still install a 100A subpanel, you just won't have a full 100A capacity.

  • 18 years ago

    I have been doing some research on this. I think I have finally figured out what I need to do, let me know what you think. I am thinking about running through the conduit, 2-#4 thhn leads for my "hots", and 2-#6 thhn leads for my neutral and ground. THan installing a 100 amp subpanel breaker box in the garage, and a 100 amp breaker in the main panel. Does this sound correct? I will also need to put in a grounding rod out at the garage itself too, is that correct?
    From what I have read, the THHN or the THWN, wire is designed to be ran through conduit. Please give me your oppinions and let me know if this sounds correct, or if I am running more wires than I need, or not enough.

  • 18 years ago

    You have the right number if wires. The wire in underground conduit must be THWN rated because condensation or leakage will result in water in the conduit.

  • 18 years ago

    The #4Cu THWN is only listed for 85A, assuming 75C terminations. You should use #2Cu (#3 is too hard to find) if you have to have 100A. Personally, I would choose 2-2-2-4 Al USE cable and protect with a 90A breaker.