Proper Wiring to Sub Panel

19 years ago

Hello to everyone! I've been reading the posts to this forum for a while now, but this is my first post. We are wanting to update my son's in ground swimming pool electrical system. It's about 10 years old and has no automated controls other than a couple of X10 controls. We are going to switch it over to an Aqua Logic system since we already installed the salt water chlorinator system and can incorporate that into the Aqua Logic controls. Besides, Aqua Logic is an amazing product that does so much. Here's the problem...the electrician who wired this pool didn't use a sub panel. This pool has 4 pumps, 2 lights, and a gas heater. He has run 2 #12 240V circuits from the house to the pool...just over 100'. He then split these circuits inside a timer to the other pumps and their controls. He also ran a 120V circuit. So my son has 3 circuit breakers in his house panel for the pool. The Aqua Logic can be used as a 100A sub panel. However, we don't need anything near that. But, running new wire from the house to the pool area would probably be impossible in the existing conduit. I can't imagine removing the existing wire and pulling new wire in that long a run. I'm almost afraid to ask this as I'm sure I know the answer, but would it be possible to use one single 40A or maybe 50A breaker in the house panel and then combine the two #12 wires to that breaker? So instead of having something like #8 or #10 wire to the subpanel, we would have 2 #12 wires in place of one #8 or #10 supplying each side of the circuit. We could then use the Aqua Logic sub panel for the pumps and 110V accessories. We do plan on pulling new THHN wiring to all the pumps and accessories from the new sub panel...along with the GFI receptacle that is required. Everything will be hard wired. Thanks for your expertise...

Comments (4)

  • 19 years ago

    to use one single 40A or maybe 50A breaker in the house panel and then combine the two #12 wires to that breaker? So instead of having something like #8 or #10 wire to the subpanel

    ABSOLUTELY NOT

    MY stance is any changes to pool wiring need to be done by a qualified electrician. This area of the codes is very strict and somewhat complex. Also there is just too much room for error. Based on your description it sounds like you wont have the capacity for 100 amp wiring, but may be able to do 50 depending on the size conduit used by the original sparky.

  • 19 years ago

    You are of course going to need a gfci max I have heard of 60A . 2 #12 parrellel a no- no CSA gives a range for conductor size when manufacturing so one set is probably a little smaller then the other would blow if any problem. Never double up to chinsc out Your 12 Conductors were probably in a 3/4 inch conduit which probably wont let you pull in the #3 or #2 you would need for the 100A a # 6 for 60 A would also be almost impossible for you to pull ; so hopefully a 1 or 1.25 in conduit was used . Any which way you need new feeds and make sure the ground wire is appropriate and bonded to your main panel connection we don't need to hear of more multi ground paths creating more deaths. Find someone to do the installation properly............

  • 19 years ago

    Thanks for the info guys...I suspected as much. I am very capable of doing this myself. There's nothing mysterious about electrical circuits, current flow, grounding, bonding, etc. But sometimes I'm not sure of the codes involved, or the proper procedures. (Maybe this means I'm NOT capable!) This pool is definitive proof that not all professionals are what they are cracked up to be. It may be safe, but none of you guys here would have ever done amything like this. This guy should be ashamed of himself. Must be the same guy that installed my neighbor's satellite dish...

    I am no fool and know my limits. Where all new conduit must be run to the pool (you were right...it's all in 1/2 inch conduit), I will probably just hire an electrician to run the conduit and install the sub panel and connect the equipment.

    I do have one other question...the chlorinator control panel we installed needs to be connected to the bonding circuit. We did that by running the bare copper lead from the box and connecting it to the bonding circuit with an approved lug. Will this suffice? Or should we have actually cut the bonding circuit and run it to the panel and then back to the other side of the cut bonding wire (and put the panel in series with the circuit)?

  • 19 years ago

    Ok now that we have discouraged you from doing the electrical connections ' The easiest part of the job and probably the least technical and the most time consuming is to run the conduit (burying etc.) is also propably the most expensive part that you could do yourself you do the calculations or get a DETAILED estimate from a Licenced Resisidential\Commecial Electrician of Materials to do the job and get them after they provide this to you to cost estimate again if you run the conduit and pull the wires.

    Bonded part of question.

    1. Bonded ground ( your second part sounded confusing maybe it was too late of night for me last night).Seemed resonable to run an appropriate size grounded wire #6 for 50A(actual capacity 60A) from box to bonding circuit with approved compression lug maybe in a pinch a KPA style lug may have met code in your area (not exceptable in my jurisdiction)

    Some area of the national code refers to the bonded nuetral I am not sure you are referring to this .........