iamscoobydoo

Pool wiring questions

19 years ago

I am planning on installing all of the electrical work for a new in ground vinyl pool and have a few questions. I did read a lot of the posts on this subject and I have a few new questions. Installation will consist of all of the following.

1 - Pool light 120V. I plan on using a 20 amp GFCI beaker to switch in house and then to deck box then to light.

1 Â Outlet for pool cleaner on the same circuit as the light but not controlled by the switch.

Everything below is installed next to the house.

1 Â 1.5 hp pump 220V 15 amp breaker to outside timer.

1 Â 5hp Heat pump 220v 50 amp breaker to disconnect switch outside.

1 - GFCI outlet for chlorinator controller on its own20 amp circuit.

My questions are

1. Can I run the NM cable straight through the house into the back of the boxes that are going to be attached to the siding on the house?

2. Do I need a disconnect switch for the pump and if so can I use a simple 2 pole switch in a weather proof box next to the timer.

3. What supports the deck box? Can it just stub up and have the PVC conduit support it?

4. I plan on a concrete deck around the pool. Does the bonding grid need to attach to the steel in the deck if they use steel?

Comments (9)

  • 19 years ago

    1. Boxes mounted on the siding to me would be a wet location. Some jurisdictions might let you slide with a roof overhang, but honestly, siding will get wet. NM can not be used for wet locations.

    2. You need a disconnect. It needs to be within sight of the pump.

    3. Must be mounted securely, many are designed to be supported by the conduit.

    4. Yes. "All metallic parts of the pool structure, including the reinforcing metal of the pool shell, coping stones, and deck shall be bonded."

    I still recommend professional help. This is one of the places you don't want to "think" you know what you are doing.

  • 19 years ago

    i have to agree with ron, get a pro. i feel comfortable working with electricity even though i am no sparky. heck, i installed a main panel and ran new 100 amp service to my workshop and a sparky friend of mine said i did a real good job, he thought i had a pro do it but i told him i used what i learned here.

    but a pool, no way would i touch it. sure, i would pull my wire and stuff, but to the specs of the sparky and he would hook it up and do the grounding, even though i am well accustomed to grounding since i have to put in ground systems for communications sites often.

  • 19 years ago

    1) The box must be sealed to the siding. The cable should never get wet. If it does it was installed wrong.
    Bottom line is YES, you can run NM cable into the back of a w/p box as long as the box is properly sealed to the house.

    2) Yes. The cord and plug are your disconnect.
    If the motor is hard wired, with sealtite for instance, you do need a disconnect. A two pole switch is fine provided it has a rating to meet or exceed the load.

    3) The conduit supports the deck box.

    4) Yes. As stated, ANY metal near or associated with the pool MUST be bonded. This includes ALL pool equipment, ladder and hand rail cups, rebar in the concrete, steel walls and members, wet niche light forming shells, etc........

  • 19 years ago

    you can run NM cable into the back of a w/p box as long as the box is properly sealed to the house.

    AFAIK, NM is permitted by code. However, though it's not required, IMO using either UF or NMC is a better practice. In my experience, all outdoor boxes eventually get wet or damp inside.

  • 19 years ago

    Thanks for the fast feedback.
    As for the outlet for pool cleaner on the same circuit as the light. Is this permitted? I will be running this back to the house and into the basement in 3/4 PVC and splicing the THHW to NM.

  • 19 years ago

    davidr,

    according to your practice then, all the romexes entering the back of a main panel mounted outdoors would be subject to moisture. Here in AZ, almost all breakers are outdoors.
    Would you use UF for all the homeruns?

  • 19 years ago

    Would you use UF for all the homeruns?

    I might. However, if the panel were in a protected location, I'd be less concerned. Most of the outdoor panels I saw in VA were on the front porch. What's typical in AZ? (Where it doesn't rain much anyway, no? ;-)

  • 19 years ago

    Most panels here in AZ are located on the side of the house where the service enters...next to the meter. There is no protection from the weather other than the box itself.

    We don't get a lot of rain, but when we get it, look out!

  • 19 years ago

    We got about 11 inches of rain last year. You probly think that don't sound like much, but you wouldn't think that if you were here the day it fell!