20 Amp time lag fuse

19 years ago

This is a follow-up to tiffer's post from November 2006. I believe I can provide more complete info to allow for a better answer.

I have a new power saw (Delta 36-729). These are the specs listed on the saw itself: 15amps, 60hz, 240v, 3HP. The plug on the saw appears to be a NEMA 6-15P, which seems to confirm for me that the saw is rated at 15 amps. I am converting a 30amp dryer circuit to serve this saw. This is a single-outlet circuit, and I intend to replace the current NEMA 14-30 receptacle with a NEMA 6-15 (two hots and ground, capping off the neutral). I was prepared to replace the 30 amp breaker with a 15 amp breaker when I read in the Delta owner's manual that the circuit should be protected by a "20 amp time lag fuse". Do I go with 15 amps and hope it doesn't trip on startup, or go with 20 amps and slightly less protection? Or any other thoughts? Thanks.

Comments (9)

  • 19 years ago

    If these are the cartridge fuses, use 20 amp FRN. When the saw is doing a heavy cut, the motor will pull more than nameplate amperage. The higher amperage and time lag help the fuse to "hold" during such temporary higher loads.

  • 19 years ago

    I just noticed that you said breaker. A 20 amp breaker will be fine. Most breakers have some time-lag built in.

  • 19 years ago

    Artilce 430 covers motors and is applicable to industrial type delta saws.
    A 3 HP motor has a full-load current of 17 amps at 230 V (Table 430.248).
    It may start using a standard 20 A inverse-time breaker, but it may trip the breaker if started repeatedly in a short period of time.
    A circular saw is actually a continuous duty load (it could run indefinitely) and it will have either integral thermal overload protection or a rated controller.
    The conductors need to be 125% of the full load current, or 21.25 A. #10 or larger is typically needed here.
    A 30 A dryer circuit should have #10 at least so you should be compliant here.
    The breaker can be up to 250% of the full load current.
    There are a couple more exceptions that allow even larger breakers (430.52(C) Exceptions #1 & 2) if the motor still trips the breaker on normal starting.
    250% would be 42.5 A, and exception #1 allows the next larger size standard value, or 45 A.
    If starting still trips the breaker you can go up top 400% for nontime-delay fuses, and 400% for inverse time breakers (68 A).
    The breaker or fuse is providing only short circuit protection for motor loads since the motor already has overload protection.

  • 19 years ago

    So brickeyee, are you stating that it would be compliant to use a 45A breaker on this circuit with # 10 wire?

  • 19 years ago

    I agree that what brickeyee has posted is correct. And I would apply those code provisions if the situation indicated a need to do so. Reading the original post and Article 110.3(B) formed the basis of my suggestions. That would be the starting point.

  • 19 years ago

    "...are you stating that it would be compliant to use a 45A breaker on this circuit with # 10 wire?"

    That is correct.
    The special articles in the NEC that see the most common use are hermetic compressors (A/C condensers), welders, and electric motors.
    Each of these items tends to have large starting current requirements, and they all contain integral overload protection. They WILL not pull an overload on 125% wires long enough to cause overheating.
    The breaker (or fuse) is only providing short circuit protection to the circuit supplying the equipment.
    The allowable increases are within the maximum fault current the wire will carry to allow for the protection to open the circuit.
    My 3 HP Unisaw is on about 15 feet of #10 with a 45 A breaker.
    With even a 40 A breaker it will not start more than a couple times in 10 minutes before tripping the breaker.
    If you want to see what the 'peak horsepower' Sears style is, the motors have a kVA locked rotor letter on them.
    You can look this letter up in table430.7(B) to kind kVA per horsepower. Divide by 746 W/hp and you can get some VERY large numbers.
    Mine is around 60 hp.

  • 19 years ago

    Thank you brickeyee. That is very good information.

  • 19 years ago

    Just remember that the 'fantasy hp from locked rotor codes is just that, fantasy.
    Sears has gotten in trouble and has a 'settlement' with the FTC about this misleading advertising.

    Rockwell (now back to Delta) Unisaws tend to have Baldor industrial grade motors.
    Many have 115% or 125% duty factors and very large reserve capacities.
    They are also TEFC (totally enclosed fan cooled) and are very well made.
    Replacements are in the $300 range (and up).
    The 1.5 hp equipment often comes with a line voltage on off switch, while the 3 hp (and 5 hp) come with low voltage controls.
    These are very much industrial grade tools.
    They should last darn near forever.

  • 19 years ago

    Thanks to all for the valuable input. After my first post, I found another option. I have a circuit in my shop with only four 110v outlets on it. It occurred to me that I could convert that ciruit to 220v and use those four outlets as a dedicated 220v circuit. Only problem is, I've checked the wiring and it appears to be 12 gauge. Am I shot down?