garage wiring problem

18 years ago

My neighbor recently plugged in a small space heater in his garage. He plugged it into a surge protecter. After about an hour, the surge protecter caught on fire. He asked me for help since I have done other work (i'm not an electrician) for him. He told me that the heater was the only thing plugged in on that circuit which may not be the truth. I took all the covers off the outlets on that circuit and did not find any thing loose. I did find all the ground wires connected to each each other with wire nuts and no connection to the outlet (green screw).

On the property their used to be a trailer house which I took down for him. The meter is on a pole with a box that has power coming in from the meter. The box has two 40 amp breakers one for the trailer which is shut off, and one for the garage. The white wire for the garage was burnt badly, The red and black that go to the breaker were fine.

The wire going to the garage is a 10/3 wire then about halfway (30 ft.) to the garage there is a junction box where the 10/3 wire is spliced to a cable with a r,b,w and bare ground which was cut. Then that goes to the garage panel. All this wire and junction box was buried without conduit.

The panel in the garage does not have a main breaker. The wire coming in has the ground and neutral connected to the same bus bar, but like I said, the ground is not connected to anything outside. There are three 20 amp and three 15 amp breakers in this panel.

What kind of wire should I replace the one going from the outside box to the garage with and how dangerous was the grounds being connected together. Also why did no breakers pop?

Sorry this post is long--I wanted to make sure I explained the problem thoroughly. Any help is greatly appreciated. P.S the outside box does have a spot for ground.

Comments (4)

  • 18 years ago

    You're risking serious lawsuit by doing illegal electical work.

    Electrical space heaters draw a lot of current, pretty much pushing the limits of a 15 amp circuit. A lot of "surge protector" strips are pretty cheesy making me wonder about their proper listing. It's quite possible the load of the heater set it on fire.

    Why on earth did you think that the surge protector burning up was somehow affected by the rest of the electrical wiring?

    There are countless problems here. The burned could be several problems. It could have been poorly connected to the terminal it was connected to, or the panel could have been seriously miswired, or there's some grounding fault that because of the other incorrect installation travelled on the neutral wire.

    You say 10/3 without indicating what type of wire. I suspect however given the general level of professionalism, that it isn't rated for outside or underground use.

    The breakers probably didn't pop because no single breaker got it's rating exceeded. The 40A breaker is oversized for #10 wire, it should have been no more than 30. I suspect some of those 20A breakers are protecting #14 wiring given the general state of things.

    I bet there's no ground rod at the structure. At six circuits, you technically may not need a separate disconnect in the garage, but you're really flaunting the issue (especially if there's room in that panel for one more breaker...)

    I suggest you and our neighbor find someone with a clue before the structure burns down or someone gets electrocuted.

  • 18 years ago

    ronnatalie-

    this garage was wired in buy the company that build the garage. they obviously did not do it correctly which I understand. He said his brother in law messed with the outside wire to splice in a 220 plug for something. I have no intensions of doing illegal work for him as I stated i am not an electrician. He asked If i could get him the proper wire to go from the box to the garage. I have no idea if he plans on installing it himself or not. I am only looking for info to give him. When i said that i've done other work for him, I did not mean electrical work.
    He told me that all the wiring was original except for that wire.

  • 18 years ago

    It gets worse and worse? Tapped in to a feeder for a 220 plug?

    Please ask this guy to get professional help before he kills himself or someone else.

  • 18 years ago

    UPDATE
    ronnatalie-

    I called him at work and told him what you said. He did not seem to concerned. I called an electrician to look at it. He got to the garage and couldn't believe it. I let him in the garage to inspect the inside. My neighbor had his dog chained inside the garage with two space heaters running. The electrician shut his power off to the garage imediately. The 20 amp breakers did have 14/2 wire, and this was the circuit both space heaters and a refrigerator were plugged into. The electrician explained to me what materials were needed to repair it and install two safe circuits for outlets. He even offered my neighbor a weekly payment plan for the labor but materials and permit had to be purchased upfront. He refused this great deal and said he would have his brother in law fix it. Same guy that already messed it up before.
    His dog is now sleeping on my couch. I really appreciate your help--I learned alot from you and the electrician.
    Now that I wasted 4 hrs of my day trying to help my neighbor for nothing -- I think it's time to crack a beer and pet my new dog!!!!