Did the Electrician Mess Up?

19 years ago

I had an electrician install a new 200 amp panel to replace the original 100 amp when the home was built in 1965. The house is all 14 wire. I noticed on the new panel, the breakers used were 15 amp, but 5 were 20 amp.

Is this wrong?

I was under the impression, 15 amp breakers should be used for 14 wire.

I believe, the electrician just replaced "in kind" what was on the original panel. The inspector just glanced at it for about 3 seconds, so he never questioned anything.

Comments (12)

  • 19 years ago

    Are you sure that the wire is all 14 gauge? Did you verify this by the markings on the cable?

    If so, you should call the electrician back. He should not have installed 20A breakers on obviously undersized wires. The bad news is that you may need to rewire those 20A circuits instead of downsizing the breakers. Otherwise, breakers tripping may become a nuisance.

  • 19 years ago

    In Canada, you can run 20A DP breakers on a circuit dedicated to baseboard heat using 14/2 wire. Perhaps the OP has a dedicated baseboard heat cc't?

  • 19 years ago

    You sure you have all #14 wire? It can be hard to tell the difference by the untrained eye... so double check the marking on the cable itself. Your electrician is an idiot if he jsut replaced whatever breaker was in the panel with the same kind. He should be able to tell #14 from #12 jsut by the feel of it.

    I find it had to beleive that a house built in 1965 would have no 20A circuits. My 1959 house has plenty of 20A circuits. Anyone know if code required 20A circuits back in 1965 for kitchens or baths?

  • 19 years ago

    They are all 14...except for the a/c....I am annoyed

  • 19 years ago

    Don't be annoyed... be angry! Call that electrician and tell him to get back and fix it ASAP! Out of curiosity, how are you determining the gauge of the wire?

  • 19 years ago

    There is no visable markings like new romex has because this stuff has a "cloth like" braided covering on it, but the wire diameter to me looks like # 14. And from working on the wires in the house in the past, #14 is very distinguishable from #12. I have never come across any #12 wires before in the house and have been in almost all the boxes by now as well as gutted several rooms. I am not sure why there are 20 amp breakers installed. Unfortunately, I do not recall what was in the panel before it was replaced, never really took notice. I assumed he replaced with what was there first, but he could have just been using breakerw he had left over from other jobs? I will find out though. And what a joke the electrical inspection is?

  • 19 years ago

    We get a fair number of negative comments about the thoroughness of inspections. It appears that many inspectors are pretty seriously overworked.

  • 19 years ago

    Did you call your electrician back? There difference between #14 and #12 is very easy to determine if you work with it frequently, but I could see people who don't work with it regularly confusing the two easily. I guess I shouldn't be surprised by anything, but I just would be very surprised that either you have NO 20A circuits in your 1965 house... and/or a licensed electrician (he was one... wasn't he?) would do such a stupid thing.

  • 19 years ago

    In some of these older homes it is difficult to determine the size of the wire. After you have handled wire for years you can feel the difference and the newer wire is even easier. But the older cloth covered wire insutaltion you describe has a tendance to get stiff and may feel like #12. Please dont be annoyed, that starts the conversation you will have with your electrician off badly and makes backing up very hard if you are incorrect and he is correct. If he was licensed he should know better. There may be a good explanation and if he is incorrect you will look a lot better if your not nasty than nasty and wrong.

  • 19 years ago

    If you have means to measure the conductors, the #14 conductor will be about 0.064 diameter while the #12 will be about 0.081.

  • 19 years ago

    This is a fire hazard if what you say is true. Get it checked out and fixed ASAP.

  • 19 years ago

    Is the old cloth wire aluminum or copper? Whenever I redo a panel from an old fusebox house that has OLD wiring I always use 15A breakers on ALL circuits. You just never know what is down the line on a circuit... It might have nice new white romex at the panel, but make go to Al wiring or knob and tube (which I have seen a lot of)... I would rather be safe than sorry. If a break then trips after the conversion, a new circuit should be run instead of using a 20A breaker on the old circuit.

    In a newer house that I can tell is ALL romex and has an old breaker panel taht I am upgrading, that is a different story... I am OK with replacing with like breakers then.