Hello all,
We are currently installing the devices (switches and recepticles) in the home we are building. As each circuit is completed, we plugged in a dropcord from the temp power pole to make the receps on that circuit hot. (We are approved for perm power, but have some grading to compelete before getting the line run to the house). Anyway, this worked just fine until we got to the bedroom circuits. When we plugged in there, it sparked - liked there was a short. We tracked it down to the point that it only happens when connected to the AFCI breaker.
Question: Is this happening because of the backfeed on the AFCI breaker? OR should we be looking for a wiring problem?
Thanks!
petey_racer
cobraguy
Related Professionals
Longview General Contractors · San Antonio General Contractors · Texarkana General Contractors · Newburyport General Contractors · Eau Claire General Contractors · Show Low General Contractors · Hot Springs Home Remodeling · Joplin Home Remodeling · Meridian Home Remodeling · Muskegon Home Remodeling · Napa Home Remodeling · Sacramento Home Remodeling · Liberal Home Remodeling · Portsmouth Bathroom Remodelers · Vancouver Bathroom Remodelerstom_in_scOriginal Author