electric outlet - install

18 years ago

Hello. I need to install six electric outlets in my renovated basement -- the wiring is all there, done by the electrician, but now we can't use him anymore and I need to take over. I've looked online and it seems that with utmost care, it can be done by a layperson. Anyone have experience with this? These would be 20 amp outlets.

Comments (9)

  • 18 years ago

    If it is just receptacles with nothing special then it is simple.

    Some of the box will have two cables and some will have one cable.
    In either case connect the black wire(s) to the gold screws, the white wire(s) to the silver screws and the ground wires to the box if metal and the green screw on the receptacle.
    Only one wire under a screw so Will need a wire nut for the ground in boxes with more than one ground.

  • 18 years ago

    Switches- some have ground terminals some do not. Is it required to have a grounding wire on a switch?

  • 18 years ago

    "Switches- some have ground terminals some do not. Is it required to have a grounding wire on a switch?"

    Not in Canada unless you're installing an isolated ground circuit, such as in a computer environment or hospital.

  • 18 years ago

    In the US if there is a ground in the box, the switch is required to be grounded.
    If there is no ground in the box, then you can operate on an exception if you do not have a metal switchplate.

    If you have metal boxes or the plastic boxes common in Canada that ground the mounting screws, you can use the metal mounting screws as a legitimate ground (for switches).

  • 18 years ago

    The wiring described by joed is safe and legal per the NEC. However, some local jurisdictions like mine do not allow "daisy chaining" of receptacles. You have to splice a pigtail to the incoming and outgoing wires and put the pigtail on the receptacle.

    The basis of this is probably that for "multiwire branch circuits" the NEC requires the pigtail on the neutral, and the local inspector has generalized this to all receptacle wiring.

  • 18 years ago

    Hello, thanks -- I am in Brooklyn, NY. With all my outlet points, two black wire and two white wires emerge through holes in the back of the metal box. In general, the electrician left things such that the black and white wires are twisted together, resulting in two sets of wires. There is no fifth wire.

  • 18 years ago

    If this is a conduit installation it could be that the conduit is the ground. The fifth wire in other words.

  • 18 years ago

    I think it must be a conduit as a very well-priced electrician did all the work. I will double check - I'd be suprised if he left out such a crucial piece of the puzzle.

    My other question is, does it matter which receptacle I install first?

  • 18 years ago

    As long as the wires are dead, not hooked up in the breaker panel, then no.