Software
Houzz Logo Print
jamesbodell

Wring bathroom questions. Easy

18 years ago

I plan to have 3 outlets in a 1/2 bathroom. This will be supplied by a dedicated 20amp circuit. I know I have to have the outlets GFI protected, but is there a restricion on which outlet has the GFI (Other than the most upstream one). Currently, the wire enters the bathroom opposite the vanity. Is it OK to not have the GFI next to the vanity?

Also, I thought about putting my lights and fan on a seperate 15 amp circuit. Is this OK? There are no windows in the room and I thought it might be nice if the lights did not go off with the gfi tripping.

Does it also have to be GFI protected?

Should I just put the lights and fan on the same 20amp circuit?

Comments (8)

  • 18 years ago

    All bathroom receptacles must be GFCI protected. So if the receptacle by the vanity is the most upstream one, then it has to be the GFCI one, with the rest of them being wired off of the load side of that receptacle.

    The lights and fan cannot be on the same circuit as the receptacle circuit.

  • 18 years ago

    Actually, I think there is the exception that if the 20 amp circuit is dedicated to just that one bathroom, you can have the lights and fan on that circuit.
    But I definitely would not have them downstream of the GFCI device.

  • 18 years ago

    Yes , If the circuit remains within the one bathroom then the lights and fan can be on the same 20 amp circuit.
    All the receptacles must be GFCI protected. Either all them are GFCI, the first one in the chain is GFCI protecting the others or the breaker is a GFCI.

  • 18 years ago

    Since it is a half-bath, I would put the whole thing on one circuit. Run the power to the switch box first, then to the receptacles. That way the lights are not on the GFCI. Make the first receptacle the GFCI and wire the others on the load side of the first.

  • 18 years ago

    So the GFCI can be in any of the 3 receptacles, as long as it is the upstream one? It does not need to be next to the vanity? That is helpful.

    The lights and fan are NOT required to be GFI protected?

  • 18 years ago

    There are some instances where the light or fan if mounted over the bathtub or shower space would require a GFCI circuit.

  • 18 years ago

    "There are some instances where the light or fan if mounted over the bathtub or shower space would require a GFCI circuit."

    But this is a 1/2 bath, so there is no tub or shower.

    Lights and fan are NOT required to be GFCI protected. All the receptacles are. The GFCI does not need to be by the vanity, but the vanity receptacles needs to be GFCI protected.

  • 18 years ago

    Thanks all, my question is answered completely!!