jack_karie

Home Load Center Wiring

10 years ago
last modified: 10 years ago

I had a quote on updating our electrical panel inside the house. It is an old fuse panel. I am trying to understand what exactly is needed in the process so that I know I am getting the best deal.

-There is NO main load center box at the meter on the power pole. This needs to be added and was in our quote for a 200 amp unit.

-The current and only main box in the house is in our quote to be replaced with a 100 amp unit.

-The detatched garage will be running a 100 amp load center for tools. This is already installed but running/burying wiring to the garage was in the quote.

I was quoted $1,800. I have another electrician who would do the install much cheaper if I were to acquire the materials. I have some understanding of load centers and NEC.

The main load center disconnect panel on the pole would have a 200 amp main breaker but would there also need to be 2 100-amp breakers in the same main panel for the sub panels? The sub panels are in separate structures so I am assuming that they would require a source of disconnect within each load center. So would this require an additional main breaker in each sub panel for disconnect purposes? I also understand there is a 6 switch disconnect rule.

One more dumb but simple question. Why are main load center panels sold in kits with breakers but do not include a main breaker? Where is the best place online to shop for electrical equipment?

Comments (4)

  • 10 years ago

    We can't tell. There are two steps really. First, you have to know what your power company mandates for the meter base. If you're upgrading to 200A service, they will typically tell you what they will do (and charge) and what they expect your electrician to do. Everything on the "service" side of your disconnect is typically governed by the power company.

    You need to tell us what the nature of all these buildings are so we can possibly give an accurate answer.

    I suspect however you have a residence and some auxiliary building and for some reason you're not running the auxiliary buildings from main residence. In this case the design above is not unreasonable. Note each structure containing more than one circuit requires its own grounding system (rods typically). In this case, the wires between the pole and the buildings are FEEDERS and do not require a disconnect at the building (single, six throw, or otherwise). You may find it convenient to put one in anyhow.

    Subpanels typically don't require a "main" braker which is why they do sell "lugs only" panel. It's also possible (with restriction) to feed a panel through a breaker installed in one of the branch circuit positions.

  • 10 years ago
    last modified: 10 years ago

    "but would there also need to be 2 100-amp breakers in the same main panel for the sub panels?" The wire needs to be protected by the appropriately sized breaker at the source of the power.

    240.21 Location in Circuit. Overcurrent protection shall be provided in each ungrounded circuit conductor and shall be located at the point where the conductors receive their supply except as specified in 240.21(A) through (H). Conductors supplied under the provisions of 240.21(A) through (H) shall not supply another conductor except through an overcurrent protective device meeting the requirements of 240.4.

    http://freenec.com/T63.html

    "So would this require an additional main breaker in each sub panel for disconnect purposes? I also understand there is a 6 switch disconnect rule." Yes, if the number of circuits in the structure is more than 6, you need a main disconnect where the cable enters the building in most cases.

    II. Buildings or Other Structures Supplied By A Feeder Or Branch Circuit

    225.30 Number of Supplies. Where more than one building or other structure is on the same property and under single management, each additional building or other structure that is served by a branch circuit or feeder on the load side of the service disconnecting means shall be supplied by only one feeder or branch circuit unless permitted in 225.30(A) through (E). For the purpose of this section, a multiwire branch circuit shall be considered a single circuit.

    225.31 Disconnecting Means. Means shall be provided for disconnecting all ungrounded conductors that supply or pass through the building or structure.

    225.32 Location. The disconnecting means shall be installed either inside or outside of the building or structure served or where the conductors pass through the building or structure. The disconnecting means shall be at a readily accessible location nearest the point of entrance of the conductors.

    http://freenec.com/T47.html


    250.32 Buildings or Structures Supplied by a Feeder(s) or Branch Circuit(s) .32 Buildings or Structures Supplied by a Feeder(s) or Branch Circuit(s).

    (A) Grounding Electrode. Building(s) or structure(s) supplied by feeder(s) or branch circuit(s) shall have a grounding electrode or grounding electrode system installed in accordance with Part III of Article 250. The grounding electrode conductor(s) shall be connected in accordance with 250.32(B) or (C). Where there is no existing grounding electrode, the grounding electrode(s) required in 250.50 shall be installed.

    Exception: A grounding electrode shall not be required where only a single branch circuit, including a multiwire branch circuit, supplies the building or structure and the branch circuit includes an equipment grounding conductor for grounding the normally non–current-carrying metal parts of equipment.

    (B) Grounded Systems. For a grounded system at the separate building or structure, an equipment grounding conductor as described in 250.118 shall be run with the supply conductors and be connected to the building or structure disconnecting means and to the grounding electrode(s). The equipment grounding conductor shall be used for grounding or bonding of equipment, structures, or frames required to be grounded or bonded. The equipment grounding conductor shall be sized in accordance with 250.122. Any installed grounded conductor shall not be connected to the equipment grounding conductor or to the grounding electrode(s).

    http://freenec.com/T79.html


    "Why are main load center panels sold in kits with breakers but do not include a main breaker?" Then it isn't a "MAIN BREAKER" load center. It is a subpanel with main lugs. They sell plenty of main breaker load centers. Sometimes, the disconnect is on the outside wall of the building, and the load center, without a main breaker is somewhere in the middle of the building.

    http://www.homedepot.com/b/Electrical-Power-Distribution-Breaker-Boxes-Main-Breaker-Load-Centers/N-5yc1vZbm30

  • 10 years ago

    Why are main load center panels sold in kits with breakers but do not
    include a main breaker?

    Because you may not want to use a panel at it's full rated capacity. Say you just want to upgrade the panel but not the service, anticipating a service upgrade at future date.

    Merchandising, especially in home centers, tends to be very price sensitive. Many people don't know or don't care about panels so they look at price. By not including a main breaker, the price is lower. For one manufacturer to include a main breaker put them at a competitive disadvantage even if they price the panel with the breaker at a lower price than the panel plus the breaker. A lot of American's can't do 2nd grade math.

    I tend to be very suspicious of "contractors" who send the customer into home centers to "save money." I can understand something like paint, "pick up three gallons of Behr Premium Plus flat paint in whatever color you like..." For something like electrical work that tends to have very specific requirements it makes no sense. If you come back with the wrong breakers, what does it he do? Stand there for an hour while you run back to Home Depot? He should be at his supply house on a fairly regular basis and would be able to pick up whatever he needs for the next job. He should have an account or enough money in his pocket to pay for the materials too. The only way it makes any sense is for him to give you a detailed list of materials including the store's item/SKU numbers. By the time he gets done writing out the list...he'd be done at his supplier.

  • 10 years ago

    I agree with mike's suspicion even though the electrician who did the upgrade of the service for our duplex rental unit did something similar. However in my case the electrician sent the parts list directly to his two suppliers and I went there and paid and the supplier brought the parts out and I loaded them in my car and delivered them to the duplex.