jhmusicinc

Look at this picture:

10 years ago
last modified: 10 years ago


The switch on the left is the sink disposal.

The switch on the right is for the underhead cabinet lights.

Neither are working, but the outlet does.

I tried resetting a couple of breakers but no luck.

Any thoughts?

Comments (6)

  • 10 years ago

    Try more breakers. The receptacles are required to be on dedicated circuits. The lighting and disposal could be shared with circuits serving other rooms.

    If that doesn't work, you'll have to do some sleuthing to see why there isn't power. Typically, one starts at the nonfunctioning device and looks to see if the hot is powered and the neutral is connected and works backwards from there.

  • 10 years ago

    No luck with the breakers; I guess I have to hire an electrician...

  • 10 years ago

    You might try looking for a GFCI under the sink.

  • 10 years ago

    The GFCI under the sink suggestion is good. In fact, I'd look for GFCI's anywhere (look in bathrooms or outside) to see if one of those is tripped. If this is older construction, these may be all strung together on one GFCI which was once permitted.


  • 10 years ago

    I unplugged and then plugged in the sink disposal. Now that works. Still no luck with the lights....

  • 10 years ago
    last modified: 10 years ago

    I have flat undercabinet LED lights that were installed four years ago, and they already failed. I assume my contractor purchased cheap units and they just did not last. You may want to verify that the lights themselves still work, and as Ron said, also verify whether there is power at the lights.

    If you want to save the first electrician's service call you will need a cheap multimeter. Even the ones they carry at Walmart will be good enough to check for 120 volts at the lights and the switch.

    If you get a multimeter and want to safely try some basic checks yourself - When you take off the dual plate/cover on the right you will be able to see the GFCI and the switch. On the lower left side of the GFCI there will be a bare copper ground wire attached to a green screw. To check your switch you would check for 120 volts difference between that ground terminal and each of the two switch screw terminals, which should be on the far right side of the switch. One terminal should have 120 volts when the switch is off, and both terminals will have 120 volts when the switch is on. If that works, then find out which breaker kills the power to that switch, and proceed from there with your troubleshooting of the lights. If you have no power at the switch, then its the breaker or the wiring for that circuit.

    Bruce