Software
Houzz Logo Print
n_rutiaga

Exhaust ductwork for 48"

8 years ago
Hi all! We (as in hubby) are installing a 48" gas Capital range along with 48" hood. Had a hard time finding the 10" roof jack and cap required but finally did at an A/C supply store. Reading the manual it specifies 10" ductwork needs to be "Class B". Big box store doesn't carry these "special" items so I am back on the hunt. Anybody know or has gone thru installation that can shed some light by sharing what they learned or by owning one in general? From the get go they are definitely different than the standard 30" connect-and-go range I'm used so there is definitely a learning curve. Thanks!!!

Comments (2)

  • 8 years ago
    last modified: 8 years ago

    You need a HVAC supply house. And the hood capture area needs to be 54”. 12” ducting would be more appropriate for that size range and CFM needs.

    Plus you will need the Make Up Air system that interfaces with the hood switch.

    This is not very DIYable without a great deal of construction experience that includes roofing and electrical.

  • 8 years ago

    A 54 x 27 Wolf Pro hood, guessing roughly an effective 54 x 24 in capture area (intake aperture) or 9 square feet, will require an actual flow rate of 90 times that or 810 CFM. Perhaps more if a real grill is included. Given a full-blown MUA system (literally), a roof top blower of 1200 CFM (free air zero static pressure) rated capability should achieve this. If there is a grill, perhaps a 1500 CFM blower is called for.

    These flow rates can be managed with a 10-inch duct and meet reasonable duct velocity values. If there is room, I recommend a silencer be included in the duct path.

    Note: if the grill or heavy duty grease-generating burners are near one end of the range, the next size up on the hood to 60 inches will be better, and then the 1500 CFM blower would surely apply. Also, continuing to use Wolf as an example, their wall Pro hoods only have a 12-inch top surface, so they likely, like my Pro Island Hood, only accommodate up to 10-inch ducts. Wolf's blowers have 10-inch duct interfaces.

    You are not limited to standard hoods or blowers, other sources exist that will build whatever you want in size, shape, and duct interface. Smaller sized up-blast (restaurant style) roof blowers can be used with whatever duct interface is suitable.

    I use a 1500 CFM rated blower on a 10-inch duct with a Wolf Pro Island Hood that is 66 inches width to obtain about 90 CFM/sq. ft., but my cooking surfaces are 36-inch induction and a Cooktek wok). While pan grilling can generate some smoke, and wokking can generate a lot of hot grease, the total volume of these is somewhat less than can be easily generated with a real grill. The heat load of a large gas cooktop is also potentially a lot greater and this affects volume and flow rate.

    Please see Figure 4, page 9 of the Greenheck ventilation guide for recommended actual flow rates using different measures. Reading the front part of this guide into the MUA section is recommended for anyone wishing to understand the principles of kitchen ventilation.
    http://www.greenheck.com/media/pdf/otherinfo/KVSApplDesign_catalog.pdf