webuser_420739870

Thermostat help.

6 years ago


Hello. I was bored today so I tried upgrading my old Honeywell heat one mercury dial thermostat, looks like it was from the 70s. I tried replacing it with one of the newer Honeywell dial thermostats CT87N (heat and AC type). I was only connecting heat. On my old unit the only three Wire connections it had were R, W, and B. I removed and connected these wires to the new unit and when I turned it to HEAT, I heard the boiler fire. I have a heating oil system.


Problem is the heat never turned off when it reached temperature. If I turn the system off I hear the zone valve close. but as soon as I turn it on it’s all heat. I tried not using the B, but nothing turned on. I am hoping the is an easy answer but I don’t want to screw anything up, right now I am just using the off switch to control it.


I do have a picture of the old wires.


Thanks

Comments (13)

  • 6 years ago
    last modified: 6 years ago

    I've called Honeywell's customer service in the past regarding hooking up new replacement 'stats and received immediate help. YMMV

  • 6 years ago

    Turn the temperature adjustment all the way to its lowest setting, 42 degrees, and give the system 10 minutes or so to stabilize. Does the heat still stay on?

    Did you follow the instructions that were packed with the thermostat? They seem pretty clear to me here.

  • 6 years ago

    I haven’t tried calling customer service but can. I did follow the instructions which basically tell you to connect the old lettered wires to the corresponding letters in the new unit. I just don’t know what the old B wire would be for and thinking that is my problem. Looking online older heat only systems only had 2 wires, R and W. I also don’t have a heat pump. The only thing I have seen is the B could be a C but I don’t want to try that and potentially break something, I also didn’t see a C wire when I replaced a unit in another zone a few years back. It also wouldn’t make sense why the old mercury unit would even have a terminal for a C.

  • 6 years ago
    last modified: 6 years ago

    Unfortunately, there wasn't much standardization in wire colors (especially early on). It was always a good idea to look at how the PREVIOUS thermostat was connected before removing it completely.


    At this point, you're going to have to go find the other end o the wires at the furnace and figure out what they are connected to,.

  • 6 years ago
    last modified: 6 years ago

    I don't think the CT87N thermostat is going to work with your oil fired boiler. Honeywell makes several variations of the old style round thermostat. The one made for heat only hot water systems is the CT87K thermostat. Page 3 shows a 3-wire installation. I believe your current B wire should be connected to the Y terminal. Both Y and W should be energized when the thermostat calls for heat. If that doesn't work then you can swap Y and W connections. The R terminal is always the 24 V power from the transformer.

    If you can't return the CT87N then call Honeywell and see if could be used. If you are going to buy another thermostat then consider buying a programmable type so you can program set back settings and save some fuel costs.

  • 6 years ago

    Is there any harm in trying to swap the wires or attach the B to Y, I am not sure if you can see the picture I attached in my original post but the wire was connected to a B terminal. I did see the heat only version had only three terminals R, W, and Y, so I contemplated trying that but was being cautious.


    Do you have any idea what the third wire would be controlling?


  • 6 years ago

    Thank you all who commented. Mike I think this is exactly what I was looking for, i did some searching and I can clearly see how to wire this on an old CT87A thermostat it has the letters of my old wires and how they get wired in that model (W -> Y, B -> W). It seems like the heat only models are compatible with 3 wire zones. I just bought an Emerson model that states they support 3 wire zone to be safe, plus that one is programmable.




  • 6 years ago

    The problem is the "B" designation has two different meaning between old and new style thermostats. You would think with 26 letters in the alphabet thermostat manufacturers could have come up with better nomenclature.

    Which Emerson model did you buy? I am skeptical an Emerson programmable thermostat will work with your system, but it is possible.

  • 6 years ago

    I bought this one https://climate.emerson.com/en-us/shop/1/white-rodgers-sku-1f95ez-0671


    Model 1F95EZ-0671, said it was compatible with 3 wire zone value connections.


    Seems like White Rodgers manufactures 3 wire zone values and Emerson now owns them. Here was the picture from the manual:



    Now the only question is whether I connect the W-->W, or B-->W and the other wire to "6", guess there is only one way to find out.


  • 6 years ago

    This Emerson model looks like it will work. Most of the default program settings have to be changed for your needs.

  • 6 years ago

    You don't think I will just need to connect the wires to the appropriate locations, you think there are more Menu settings that will need to be adjusted? Can you point me to the sections in the manual for this or if you know off hand. I just need to know what I should be looking for to change. I do appreciate all of your help on this.

  • 6 years ago
    last modified: 6 years ago

    Google on Model and get manual.

    Manual


    PS I didn't read it to see if there is a separate Installer's Manual.