Narrow junction box and GFCI

3 years ago

Hello,


I had an electrician install GFCI receptacles (as per their recommendation) due to my homes older electrical wiring.


I also have asbestos in my walls so I want to avoid ripping it out and replacing the 2x boxes with a larger one.


I drywalled over the existing wall in my sons bedroom and extended the boxes with extenders (as pictured, extension around GFCI receptacle to show clearance).


I am aware back stabbing wires isn’t typically recommended. It is what the electricians did and wonder if it creates more clearance here?


The fit was tight when they did it but the insert shrinks the gap even more as it goes inside the walls box.


I also have considered finding a smaller GFCI receptacle. I prefer not to rely solely on electrical tape to provide protection here as is.


Maybe the clearance is fine?


Hoping someone is able to offer some insight.


Thank you






Comments (12)

  • 3 years ago

    Your description isn't entirely clear, but, if your concern is possible arcing from the side terminals to the metal box/extender, a couple of wraps of electrical tape will prevent any problems.

    P.S.: What makes you think you have asbestos in your walls?

    J K thanked kudzu9
  • 3 years ago

    Thanks for the response.


    yes, arcing is one of the main concerns.


    As far as asbestos, I had the walls tested.

  • 3 years ago

    Backstabbing to a single outlet is probably ok. I used plastic extenders that weren't an insert in my kitchen. I'm not familiar with the ones you used.

    J K thanked Seabornman
  • 3 years ago

    Thanks for the comment. The backstabbing was done by a licensed electrician/s. However, they werent the greatest and did a couple questionable things.

  • 3 years ago

    Nothing wrong with the back stabs on those gfi’s. What is your issue not wanting to rely on tape?


    If the connections are tight and they're tape wrapped, you're not going to have any issues.



    J K thanked Dave
  • 3 years ago

    Thanks for the response.


    Initially I felt ok about wrapping to protect but then started reading and people have mentioned that tape is more of a ”hack” (fire hazard, degrades over time etc.)


    I am just trying to err on the side of caution but also have to be realistic.



  • 3 years ago

    Im a licensed electrician. we have always tape wrapped outlets that are in metal boxes. sometimes we don't if theres a lot of room. Nothing wrong with the practice. Most GFI’s are meant to have the back stabs used. Thats the only way i do them.


    The tape isolates like actual wire insulation does. its not a fire hazard in any way. not that id start worrying about the old wiring, but new tape is going to insulate better than the old wire insulation.


    Get some nice super 33 tape if you want the best.


    Some of the things you're reading sound like they come from uneducated home owners and not actual electricians.


    If the box, and actual outlet is tight, its not going to move unless toy hit it with furniture or something drastic.


    I really would not worry. There is no fire hazard here that i can see.


    J K thanked Dave
  • 3 years ago

    Thank you for the extra clarification and reasurance. That makes alot of sense.


    lots of great pieces of information you have provided.

  • 3 years ago

    Thank you, I picked up some quality tape today and will be wrapping it.

  • 3 years ago

    The receptacle in your picture is a 'back-wired', not a 'back-stab'. Big difference. A back-wired has the wires held by a screw-tightened clamp. Very secure when tightened correctly. A back-stab has the wires by a marginally effective spring clip which is prone to failure to provide a proper electrical connection.

    J K thanked HU-178658043
  • 3 years ago

    Thanks for the clarification.