Installing GFCI in parallel on another circuit

18 years ago

Hi all - I'm not familiar with all the technical terms, so apologies in advance if I'm not using the right terms.

I want to install a GFCI outlet for a fish tank. The circuit the fish tank will be plugged into has a refrigerator as well as another GFCI-protected circuit at my kitchen countertops downstream of where I need the GFCI installed.

The simplest install would be to just install the GFCI where I need it, and the countertop GFCI will daisychain off it. The problem is, the refrigerator's outlet will now also be GFCI protected. Is this a safe install?

What I would really like to do is GFCI-protect only the fish tank's outlet, and leaving the refrigerator and countertop GFCI as is. I'm thinking the best way to do this is to splice the black wires and the white wires together at the outlet I'm replacing, then connect these to the "line" connectors of the new GFCI outlet, in essence connecting the GFCI in parallel to the circuit. Is this an acceptable way to install the GFCI?

Thanks!

Comments (8)

  • 18 years ago

    Follow-up to the above - basically, I don't want to add any downstream GFCI protection, and want to just leave those outlets as is. I just want to add protection to the outlet I am replacing.

    Thanks!

  • 18 years ago

    Yep, just use pigtails off the lines and connect to the GFI. The GFI Receptacle will have a line- load side. Just connect the pigtails to the line side and the rest of the circuit will stay the same.

  • 18 years ago

    "The circuit the fish tank will be plugged into has a refrigerator as well as another GFCI-protected circuit at my kitchen countertops downstream of where I need the GFCI installed."

    You are NOT allowed to use the kitchen wall-counter circuits for this.
    Run a new circuit.

    I have had salt water aquariums for many years.
    They deserve a dedicated circuit(s) for lighting and often the pumps.
    The price for something else turning off the circuit is too high.
    You also need to ne very careful with GFCI circuits.

    While they provide a higher degree of safety, they can also trip on leakage currents (especially for salt tanks) that will kill everything in the tanks.
    The leakage current COULD be a hazard to you, but killing the pumps is a sure hazard to the tanks.

  • 18 years ago

    Thanks, everyone!

    Brickeyee - can you clarify "You are NOT allowed to use the kitchen wall-counter circuits for this"? Is there code against this, or are you just saying it would be risky given the potential loss of livestock in the tank in the event someone plugs in one too many blenders in the kitchen?

  • 18 years ago

    There are codes that prohibit what goes on an appliance/ countertop circuit. A wall outlet would be allowed on the counter circuit if it is in the dinning room or kitchen. But it sounds like you are just replacing an existing outlet and not tapping off the counter circuit to add an outlet in another room. you can plug what you wish into outlets. If the equipment were mounted in place it would require a different circuit. I think what he is saying is you can't tap a kitchen outlet to serve a new outlet in the living room/ other room and that a dedicated circuit is recommended.

  • 18 years ago

    It is a code violation. Nothing else is allowed to tap off the kitchen circuits. He is saying your best bet is to run a new circuit-least risk to the fish since there is virtually no risk of overloading the circuit

  • 18 years ago

    spencer_electrician - this particular wall socket is in the Breakfast Nook (which, I guess, is considered a Dining Room, even though we have a separate "formal" Dining Room.) You're correct - I would be just replacing an existing outlet and not adding another one. With this be compliant, then?

    But I guess as Brickeyee mentioned - it's just a better solution to run a dedicated circuit for the fish tank.

  • 18 years ago

    Legally you could install an outlet off the counter to that location. However since you want to do it right and not just what is minimum code, a dedicated would be best. Then again if the tank only uses an amp or two, it may not be a problem. Depends on the equipment. With the refrigerator already hogging the counter circuit, a new circuit is a good idea. Especially if it is not a terribly difficult run to the panel.