Fused Outlets?

18 years ago

My sister, living in a 1920's building in Chicago, had a lighting circuit protected with a 30amp breaker and while running a 10-amp heat gun "burnt out all the bedroom outlet boxes". I don't know how old the receptacles were.

The electrician she called replaced the breaker with a properly sized 15 amp'er, I assume the wire was 14AWG, and said, translated through my sister, " there were little fragile pins connecting the outlet boxes (?), which he replaced." Anyone ever hear of a fused outlet?

The guy didn't replace the wire.

Should she have the wire replaced too? I'm concerned it could have been damaged and now has a lower current capacity, below 15 amps.

Thanks,

Bill

Comments (3)

  • 18 years ago

    If a licensed electrician thought the wire was ok, I wouldn't worry. The only damage that could have happened to the wire is to cook the insulation and make it brittle (more likely to fall off) and the electrician would have noticed that when he was working with it. Nothing could have reduced the current carrying capacity of the wire.

    The fragile pins were probably the spring-loaded "back stab" connections that are provided on some receptacles for quick wiring. They are adequate to pass the UL tests but not very reliable and this forum has had many horror stories about problems they caused. If they were making poor contact a heavy load could cause them to overheat and lose what spring tension they had. Many people ignore the push-in "back stab" holes and wire to screws (or on some devices screw-clamped holes) which make a more reliable connection.

  • 18 years ago

    Backstabs are especially bad when any sort of movement is present. This ought not to happen, but my 1970's tract piece of poop Ryland Home has the boxes not extended out anywhere near the finish surface and the morons use the switch plates to provide the mounting rigidity to the outlets. I can't tell you the number of backstab failures I've had as a result.

    I've been gradually converting my hole house over to decora and screw terminals (generally whenever my wife repaints a room, she always gets paint in the darned receptacles anyhow).

  • 18 years ago

    Thanks much for the replies. I won't worry then, though I hope the guy she called was licensed. She mentioned he was the guy she uses for all her electrical work, so I assume he'd been inside the panel before and not noticed the 30-amp double breaker with one smaller gauge wire attached to it. Maybe I'll still worry afterall.

    Bill