Electrical Circuit Wiring

18 years ago

Is it possible to run two 20 amp circuits using 10-3 romex. I want to run power to a batting cage that will require about 150 feet of cable. On one circuit I want to control 2 500 watt lights and use the other circuit to control the pitching machine and possibly a small above ground pool pump. If I use the same ground and neutral for both circuits and a separate hot wire for each of the circuits, that won't overload the neutral, will it?

Comments (7)

  • 18 years ago

    What you suggest will be fine. Just make sure that you use a double pole 20A breaker and that each pole is on a different hot bus in the panel. Because each pole is on an opposite leg, the neutral current from each leg cancels out. If you had both poles on the same leg, then the neutral current would be additive instead of subtractive, and then you'd have a problem.

  • 18 years ago

    If they use a double pole breaker then they would be on seperate phases..be tough to same phase a 2 pole

  • 18 years ago

    "If they use a double pole breaker then they would be on seperate phases..be tough to same phase a 2 pole"

    The plastic divider is every 2 lugs down the bus on most panels which means a double pole breaker can easily be put between 2 successive dividers, not bridging them.

  • 18 years ago

    Parker_j, depending on what the pitching machine requires, you may not need to use 10/3, can probably use 12/3. It will save a few bucks...

  • 18 years ago

    Don't forget the GFCI breakers. Place them at the end of the run and if for any reason the neutral opens they will trip, not designed specifically for that but they do. Code probably will require one on the plug anyway. Use 20A units, I don't know if all the codes have changed yet to require them but they will.

    I am making the assumption this is in the same building inside, if outside you need to use UF (Underground Feeder) cable.

  • 18 years ago

    I think gil means to use GFI devices, NOT breakers. Breakers go in the panel at the beginning of the run. A GFI receptacle is NOT a circuit breaker.

    Also Parker, I hope you scrapped the idea of including the pool in this wiring scheme as has been strongly suggest on other message boards.

  • 18 years ago

    As Petey says, you can not use the proposed wiring for the pool circuit.

    You will need GFCI protection (GFCI by the way has no freaking clue if the load side neutral is open unless current from the hot lets is faulting somewhere else).

    If you are using a multiwire circuit the GFCI device must either be a 220 w/ neutral device or it's not going to work. The other option is to install it after the circuit ceases to be multiwire (split off at the end of the run).