Is this likely not to code?

17 years ago

In the house I bought, the DIY home electrician ran about 50' of romex from a sub-panel inside the garage, across the entire width of the garage, up one exposed wall and into a ceiling. This isn't to code is it? Wasn't he (and I'm assuming it was a he, as I haven't met a woman this stupid) supposed to either run the cable inside a conduit, or use metal sheath flex for exposed romex?

Comments (6)

  • 17 years ago

    How is it exposed? If it is stapled properly to the side of the stud and framing it is likely fine.

  • 17 years ago

    Not a problem unless you live in an area requiring conduit for everything.

  • 17 years ago

    I live in California - we require just about everything I think....hehe. It is basically stapled to the top framing of the garage door frame as it tranverses the width of the garage.

  • 17 years ago

    Well I have met plenty of women that are at least that stupid and also a lot of men so gender when it comes to stupidity, at least in my experience is not a factor.

    The only way you are going to settle the question of being to code or not is to talk to the local inspector and not just go off on some rant about stupid people. You might want to check and see if a permit was required to do the work and whether or not it was actually applied for or issued, if not you might not want to get the inspector involved.

  • 17 years ago

    California rules aside, the main code rule concerning this is that NM-B (Romex) can't be installed where it's subject to damage. This is a purely subjective thing, but it's pretty obvious in a garage there are many things that can damage cable near the floor, like shovels, misc tools, and "stuff" consisting of who knows what. At eye level there is certainly much less that could damage cable as it's above most things, including easily accessible shelves with things that can damage the cable. This is why most building departments require NM-B in a garage be behind drywall if it's less than 4 feet above the floor.

    While not pretty and any Cali rules aside, there's nothing particularly wrong with what you have. If the wire isn't where you will be putting things it's probably OK.

    As to that "metal sheath covered stuff", it has the same rules for not being installed where subject to damage as NM-B. If damage is likely, it needs to be in non flex conduit.

  • 17 years ago

    Thanks itsunclebill, that is an informed and intelligent answer, unlike my sad and humourless question. The Romex is indeed 7-8 feet off the ground and never gets below that level, and is clearly out of the way of any "activity" or weather elements. That being said, I won't worry as much about it as I thought I may have had to, and when an inspector is somewhere in the vicinity, I'll have them take a look.
    And regarding women, all the ones I know wouldn't attempt to install something like this unless they knew they were doing it right. The same can't be said for alot of men I know, but that's just me.
    Cheers