correct wire gauge

19 years ago

Good evening all, Got a question concerning my mig welder. its a millermatic 150 230 volt. We recently moved into out 1st house and the pole barn we have did not have the correct receptacle for the miller, so I was going to correctly wire it for the miller, I went to http://www.millerwelds.com/om/o1310f_mil.pdf to look up the correct gauge wire for my welder on page 7 it states it needs a 30 amp breaker, and at least 14awg. Now I am no master electrician but for a 30 amp breaker should it not be at least 10 gauge? so that is my question. the run of wire will be around 35 feet. Thanks everyone

Comments (8)

  • 19 years ago

    If the welder is plugged into a receptacle then YES, use #10 on the 30 amp breaker.

    OK, I know all the master electricians will come on and quote all sorts of parts of Art.630, and say that welders can be wired with smaller wire, bla, bla, bla.

    IMO this is not wiring a welder. It is wiring a 30 amp receptacle in a pole barn. Who knows what will get plugged into it later.
    Yes, the plug and receptacle are the disconnect for the welder. But the receptacle can also be the disconnect for MANY other things as well.

  • 19 years ago

    actually petey racer, that is a very good suggestion and well thought out point.

    I would have to dig into article 630 (is is actually 630) to verify or dispute the sizing but petey's point is valid, especially since it is a residential use. The difference in cost between #14 and #10 is not so great that you cold retire on the difference so listen to petey on this one.

    sometimes we do get caught up in the technical and exacting points that aren;t neccessary.

  • 19 years ago

    Thanks fellas for the confirmation, just wanted to be sure. Also, is there any benefit to going with even a larger gauge wire #8, #6 ect.. over #10 while still maintaining the 30 amp breaker. I know the longer the run is the more of a drop in voltage there is but I was just curious. Thanks again

  • 19 years ago

    No benefit going to a #8 or larger unless your run is over 75'.

  • 19 years ago

    For the record, there are special rules for welders (yep, section 630). Without doing the math, the numbers given in the Miller manual look like they could well be correct. So, they're not crazy, actually.

    But, listen to Petey. He told you the smart thing to do. Use #10 with the 30 amp breaker.

  • 19 years ago

    Thanks again fellas, pretty much what I thought but I like some other opinions just to be sure.

  • 19 years ago

    if you want to get into riduculous use of theory, the bigger the wire the better. Simple as that. The larger the wire, the lower the resistance which is better. The problem with that simplicity is the gains are so minimal and provide no true benefit that you don;t go beyond what is actually needed.

    So, stick with the #10. It is all you need.

  • 19 years ago

    I would add that it's important to use the overcurrent protective device called out in the installation instructions. That you don't oversize. But the wire can be safely oversized in almost every case.