matt_r_gw

Is this installation look safe and/or code

19 years ago

I electrician is wiring my bathroom, and some things looked strange. My wife insisted upon having sconce lights on either side of the mirror. However, there was a vanity cabinet on the opposite wall bathroom that consumed the wall cavity space (as shown on the second picture). So the carpenter built out over the studs using 2X4's and 2x3's layed flat onto the existing studs to "build" out the wall so a round metal box could fit for the sconce. He said he ran out of 2x3's, so he used 2x4's he had already. It may have been a bit cleaner looking if he just used furing strips or something not quite so wide. These studs are not really for support, but just to get the wallboard attached to. On the first picture, the box was screwed into a stud and the bracket removed on the box as shown on the second picture. Is this OK? Does anything else not look correct? The carpenter redoing the bathroom hired the electrician (his friend) to do this.

{{!gwi}}

{{!gwi}}

Comments (12)

  • 19 years ago

    I think you meant that the built-in cable clamps are removed from the second box. I do not understand exactly why the romex connector is reversed in the second box. It could easily have been installed the other way. But I have installed them as pictured if there was no practical alternative. The snap-in connectors were not available until recent years. I see no real problem with the installation.

  • 19 years ago

    First off, the box in the first pic is a not side strap box. The box in the second pic is.
    Same goes for the internal clamps. The first box has them, the second box does not.
    Nothing was removed from the either box.
    Not all boxes are the same.

    I must say though. This does NOT look like the work of an experienced electrician. The the use of those funky DIY ground tails, those plastic staples AND the backwards NM connector are clues.

  • 19 years ago

    It's adequate but not "pro"

  • 19 years ago

    petey, there is a couple of areas around me that require plastic NM "staples". They don;t even allow the staples with insulator as acceptable so claiming lack of "pro" is a bit harsh possibly.

    and "funky" ground tails? I use pre-made tails all the time although not the type with the wing nut included. When you have a boat load of boxes to trim out, that is a lot of tails to make. There is also a tail made with 2 leads so you have a tail with a stake on to attach to the device. Handy in my book. (I don't do NM though and I do understand the methods of the continous ground lead wrapped around the various screws situation y'all do do)

    Now as far as the backwards NM connector; I'll have to agree on that one.

    Now the one thing that looks wrong to me but I can't tell for sure but it looks,in the top pic that the face of the box is even with the stud which would not be kosher. It should be set out so the face of the box will be flush with the sheetrock.

    Could be simply the perspective though not showing the set out of the box.

    my personal preference is a 4" square box with a round tile ring with the proper depth ring for the sheetrock being used.

  • 19 years ago

    Are metal staples better than those plastic ones? I saw the plastic ones in the store a month ago, and thought they are kind of neat, had 2 nails. What is the down side to them.

  • 19 years ago

    The plastic ones with the nails are a PIA to install IMO. Simply my opinion.

    Also, you cannot stack two cables under one staple. This forces the use of cable stackers if more than two cables run down a 2x4.
    These things really do scream DIY. One of the key points is that the inexperienced stapler cannot over drive a staple damaging the cable.

    If my area actually did require them I would petition the local board to allow something else. I would find it absurd to not allow at least plastic coated metal staples.

    Luckily my area still allows old school metal NM staples.

  • 19 years ago

    Often when stapling on "running" boards, the nails at the joist dictate stapling at other points. The boards often deflect in the unsupported span when driving regular metal staples and the plastic "two nail" drives easily. No splitting of the boards near the end either. I try all the new listed materials and use whatever works best in a particular application. The plastic is not my usual first choice.

  • 19 years ago

    Perhaps using the plastic staples is a regional thing... ???

    Almost never seen anything but in a residence in MN.

  • 19 years ago

    Personally I like the plastic staples for the reasons mentioned above - It's almost impossible to damage the cable. Even the round -3 cables are hard to hurt, since the plastic gives a bit. They also seem to drive easier, esp. when I'm in a tight space and can't get a good hammer swing going. The nails are smaller and sharper than regular staples. I hate using staples now.

    But then, I'm a DIY. ;-)

  • 19 years ago

    On the "This Old House" PBS show, they showed work done by Galant (sp)? Electric. This guy is the epitome of neat work. They showed two side-by side 200 AMP panels, with the cables neatly arranged, no twists, perfectly parallel. He used the plastic staples. If they're good enough for him, they're certainly good enough for me.

  • 19 years ago

    Is the box in the first pic in contact with that copper drain line next to it? That will cause corrosion eventually...

  • 19 years ago

    Speaking of staples, in the top photo, I don't see anything securing the cables above the box. I thought that was OK only when fishing cable. Of course there might be staples or something within 12" but above the frame of the picture.