problems since lightning strike

18 years ago

Hi, I got lots of help at this forum wiring my pool pump and a convenience outlet back in 2005. Everything had been operating well since that time until a lightning storm last week. The existing circuits are as follows- a 3 wire 220 volt circuit from a 220 volt gfci breaker along with a seperately wired 110 volt convenience outlet. I followed the advice I had received here. I used 12 guage indvidual conductors in 3/4 conduit.

Heres what happened. Big lightning storm. Found that the 220 volt gfci for the pool pump had tripped. When I pushed the bar to reset I got a large spark. I initially thought it may have been because I did not push the tabs to the left before resetting. The second time I tried to reset, it did and the pump began to operate but i noticed a burn mark near the white test button and found that when pressed the breaker would not trip. I assumed that i had simply burned out the 220 volt gfci. I purchased a replacement, installed it like the original and turned it on. The pump operated. When i pressed the test button big spark and burn mark next to the white button. Again the pump would operate but no gfci protection. I could not understand what the issue was. After checking the leads with my test meter I discovered that when the 110 volt convenience outlet is on I have trace current flowing back through the leads to the pump(about 15 volts on my meter) I do not understand how this could be since each circuit is isolated. I thought i had a short in the wiring- so i replaced all of it. Having done that the issue still exists. When i turn on the convenience outlet circuit the meter shows that I have current flowing through the pool pump circuit. I am putting one test lead on the neutral bar the other one the turned off pool breaker, at this point I'm stumped. Everthing operates but i don't want to install and burn out another gfci breaker. I'm planning on calling in an electrician co-worker to help trouble shoot the issue but I am frustated and open to ideas.

Comments (8)

  • 18 years ago

    Probably time to start taking things apart and running a megger on the wiring and even the panels.
    Lightning can induce high voltage and damaging currents into electrical wiring.
    The fact that anything was damaged means the voltage and/or current got into the wiring.
    Even magnetic filed coupling from the lightning (made worse by long runs) or the current dissipating into the earth (your wiring is a much better conductor than soil) can result in transient voltages that can damage equipment.

  • 18 years ago

    Tell us more about the spark. Between what and what?

    Are you sure you have the new GFCI wired correctly?

    If you install another GFCI make sure it works before any load is connected.

    If this is a high-impedance meter it may be reading stray voltage that doesn't have significant power behind it. You use the word current, but that is measured in amps, and you are measuring volts, so we don't know that there is any measurable current.

  • 18 years ago

    Thanks for the replys. The spark I got when re-setting the original GFCI breaker appears to have come from within the breaker by the white test button...it left a burn mark. The spark was substantial. I purchased a replacement GFCI thinking the original had been damaged by the lightning strike. I installed it identically to the original, white pig tail to the neatral bus bar and the two load wires to the load (outside) conection on the GFCI breaker. When pushed to the on position it operated the pool pump. When I pressed the test button I got a spark like i did with the first one. At that point the breaker would operated the pump but would not trip when the test button was pressed. I also observed the same burn mark near the white test button. At this point I removed the GfCI breaker and in a process of trial and error found that when the 110 volt convenience outlet that runs in the same conduit is on I can detect measurable voltage on my test meter when I put the leads on the pump wire and the neatral bar. In my thinking there is no reason for their to be measurable currrent coming fromthese wires. The issue does not exist in the reverse. With the pump circuit on there is no detectable voltage in the convenience outlet circuit. Originally i thought there must be short in the wiring somewhere in the conduit. I replaced all of it and inspected the wiring i removed and could find no obvious damage. when i had it all re-wired I detected the same issue I had before replacing the wiring. Obviously i am missing something. For the life of me I can not see any reason that I would be able to detect voltage from the pump wire when the other cuircuit is energized. At this point I think I am misinterpeting the data.for the time being I pulled the G.F.C.I. breaker to get the pump running I know everthing was operating correctly before the lightning storm. Even if the voltage is "stray" from the long companion run in the conduit would that cause the G.F.C.I. to burn out? thansk again for any advice.

  • 18 years ago

    At first this sounds like it has nothing to do with your problem, but bear with me.

    A capacitor doesn't have 'resistance', it has 'reactance', but that can also be measured in ohms, and, as long as the frequency of AC remains the same (which it does), the reactance will remain the same, and hence a capacitor will appear to act as a resistor.

    A capacitor is manufactured, basically, by taking two conductive materials and putting an insulator between them.

    If we run two pieces of wire (conductive materials) next to each other, with insulation (an insulator, we hope) in between them, we've accidentally built a capacitor, and since this is an AC circuit with a fixed frequency (60Hz), we've built a high-value resistor.

    Therefore, there is a high-value resistor between the wiring to your "convenience outlet" and the pool pump circuit. It's a high-value resistor, so there won't be very much CURRENT available, but the open-circuit voltage could understandably be relatively high. (open-circuit, in theory, should be the full 120, but your meter will pull a tiny, tiny bit of current and drop it. The highest I've ever measured was 70).

    The pool pump might seem, at first, to provide a "load" for this capacitively-coupled voltage, but since BOTH sides of the pump motor are disconnected (it is, after all, a double-pole breaker), this is not the case.

    In any case, finding "stray voltage" on your pool pump circuit when another "independent" wire directly next to it is energized does not really represent a problem.

  • 18 years ago

    I had a second set of eyes look over my wiring today(maint. tech with some electrical experience) with a phone consult to a co-worker electrician. For what its worth the "stray" volatage does not appear to be the issue. That voltage shows up regardless of which wire is carrying a 110 current. Just to check I disconected all the wire and ran 110 volts through each one and found the "stray" current showed up on all the other wires in the conduit. Interestingly (at least to me) if I feed the pool pump circuit (220 volts) there is no stray current. If I feed just half the pool circuit, either 110 side then the other wires show the "stray" current. I'm sure their is a reason for that keeping with the explanation above about creating a resistor in the conduit by running energized wires side by side in a conduit. So if the "stray" current is not the issue the elctrician suggested there may be a problem with the pool pump motor. My friend checked both sides of the leads that run to the pump and his meter indicated that it was drawing 6 amps on each side. He beleived that if the motor had a short that it would show up drawing many more amps. I regret not testing the GFCI before attaching a load. At this point I'm consdiering the possibility that the replacement GFCI was faulty......that just does not seem likely. I'm going to get a replacement and test it without load and then go from there. Does anyone have any thoughts on how the electric motor could cause the GFCI to fail the way I have previously described. I'm thinking even if the motor did have an issue the GFCI should trip not arc out.

  • 18 years ago

    I'm sure their is a reason for that keeping with the explanation above about creating a resistor in the conduit by running energized wires side by side in a conduit

    Yep.

    You've now got two "resistors" - one from leg A and the other from B, both the same value, with the wire you're measuring (the 120 wire) in the middle.

    So draw two resistors of the same value in series. Put +120 on one end of the chain and -120 on the other. The middle voltage is 0. Since the voltage on A is always opposite that on B, they cancel each other out, and you get 0.


    ---


    There is no official "normal" operation mode of a GFCI that causes the problems you describe. A GFCI is a protective device that is specifically designed to deal with faults of all sorts elsewhere in the circuit - and the only thing it's "supposed" to do when there is a fault of any kind is trip. Simply turn off, non-destructively, and wait for you or some other kind soul to fix the fault.

    I've seen the failure you describe occur in GFCI receptacles, usually accompanied by a lot more spoke, sparks, occasionally some flames, and always a tripped breaker - but that usually occurs when someone gets some line/load wires crossed in screwy orders, and that wouldn't seem to apply with a GFCI breaker - especially one that has been operating properly for some time.

  • 18 years ago

    I guess all of this leads to replacing the G.F.C.I. breaker again. Is there anything I can do (besides testing the breaker with no load) to avoid a repeat of the arc out......What I'm asking is assuning the GFCI operates properly without load and then I hook up the pump (2 110 leads). Is there any condition in the pump (assuming that something may be wrong with the pump motor) that would cause the GFCI to do anything other than trip?

  • 18 years ago

    Installed a new GFCI breaker today. Tested it with no load, no problems. Then we hooked up the pool pump and turned it on with no problems. Tested the GFCI, again no problems. It appears the issue was a defective replacement GFCI ( the first was ruined by the lightning strike). Thanks for the responses, it was a learning experience for me.