What capacity wire do I need for this?

18 years ago

I'm investigating a solar panel array on my home, and have decided that, if I were to proceed, I would have 20 panels mounted.

Their peak ratings are 200 watts at 27 volts.

I found online a formula, don't know if it's right, watts x volts = amps

so that would be about 7.4 amps.

Is this right?

Also, if it is right, would 12 gauge insulated copper wire be adequate to transmit the power from these panels (connected in series) to an DC/AC inverter?

And finally - what capacity requirements would I have to worry about for the inverter? I need it to convert the power to standard 120 volt, like I get from the power company right now.

Comments (5)

  • 18 years ago
    last modified: 11 years ago

    You've posed a big set of questions here--basically asking for an overall solar system design. I'll take a rough crack at at least some of the issues.

    One critical piece of missing information is whether this will be a grid-tie or an independent ("off grid") system. Because you've noted that you want to produce usable 120V power, I'll assume that it will not be a grid-tie system. (That's when you generate power and "sell" it back to the power company.) If I'm wrong about that, toss out all of the suggestions below.

    Twenty 200W panels produce about 4kW (4,000 watts). The word "about" is intentional because, when estimating peak sunlight yield, you should figure on only about 80% of rated output. (That tends to incorporate loss of efficiency over time as well.) However, the true peak yield in the best of sunlight can be in the order of 1.2 times listed output. The high panel output values are used to estimate wiring requirements. (If you read the fine print for the panels, those high/low specs will be disclosed.)

    27-volt panels are typically appropriate for charging 24-volt battery systems. (Keep in mind that to charge a battery, the source power needs to be higher than the nominal voltage of the battery.) So, in figuring your wiring ampacity needs, the conservative way to estimate is to think in terms of 24 volts.

    So....4kW at 24 volts produces a current of about 170 amperes if all of the panels are wired together in parallel. Number 12AWG wire? Not even close. That'd fry in a NY minute. You'd need something like 3/0 or 4/0 to carry the full output of the array at 24 volts.

    If you connect all of the panels in series, you'd be transmitting about 540 volts (20 x 27 volts). [Here, I'm taking the more conservative approach of using the higher voltage.] Unless you're looking at equipment I'm unaware of, 540 volts will almost certainly fry the panels and I'm doubtful that you can find a reasonably priced charge controller built to handle 540 volt input and 24-volt or 48-volt output.

    What you need, IMHO, is some good overall design assistance to determine the best options.

    Shooting from the hip, here's a quick pass at a possible design that attempts to optimize wiring and equipment at about the scale you propose:

    1. Consider subdividing into two arrays of about 2kW each. To reduce current flow (and wiring size), consider wiring each in a series/parallel combination so that you have a 48V (nominal) DC system. Now you can use more moderate wiring--say, #4AWG copper, depending upon distance. At 24V, #1 or #2AWG copper might be the size of choice.

    [Keep in mind that distance and voltage drop are extremely important in carrying solar-generated DC power. Whereas AC house wiring can tolerate voltage drops of 5% or more, it's best to keep DC voltage drop to 2% or less.]

    2. Use ("stack") two charge controllers--one for each array.(That's mostly because controllers of this scale are relatively economical today.) A 24-volt battery bank would probably work pretty well at this sizing and, once again, it corresponds well to available inverters. A 48-volt bank could also work.

    3. As for the inverter, you'd probably be looking for something in the range of 3-5kW continuous output capability. (The surge rating might be in the neighborhood of 6kW-9kW.) To duplicate (or improve upon) grid power, use a true sinewave inverter.

    Because I don't know the actual requirements of your proposed system and don't know your sunlight/climate zone, or the intended usage patterns, please, please take this only as a rough example. It is not a complete competent design and many other configurations are possible!!!

  • 18 years ago
    last modified: 11 years ago

    You should be aware that there is a big pile of NEC requirements for a solar electric system. To build a legal system is going to require a great deal more knowledge of the nuts-and-bolt rules than your OP suggests that you have, and that you are going to be able to learn from forum posts at forums like this.

    I don't know of a good reference for this information. The best I can suggest is studying the relevant sections of the NEC, and the last several years of issues of Home Power magazine. (They usually have a good column each month about code issues.) Either that, or hire a pro to do the job, or (if he's willing) to oversee the work you're doing.

  • 18 years ago
    last modified: 11 years ago

    "I found online a formula, don't know if it's right, watts x volts = amps"

    For a DC load, watts = amps x volts.
    This is high school physics level electricity.

    Read up some more or hire someone.

  • 18 years ago
    last modified: 11 years ago

    Thanks for all the advice, terribletom and solarpowered!

    brickeyee - As I said, I didn't know if it was right, and as far as it being high school physics, I feel it necessary to mention that none of my classes during high school ever touched on electricity, nor did they do more than 'mention' what many people consider to be basic physics. Everything I know about these subjects comes from talking to others, whether online or in person, and much of it is probably bunk (such as 'watts = amps x volts').

    I'll take the information you have all given me into consideration, and figure out what I'm doing next. This is all still theoretical for me, and it might amount to nothing, but it's worth investigating.

    If I have more ideas on it, I will post a new topic with more information, such as grid-tied or off-grid, etc.

    Thanks again for your help.

  • 18 years ago
    last modified: 11 years ago

    >I feel it necessary to mention that none of my
    >classes during high school ever touched on electricity,
    >nor did they do more than 'mention' what many people
    >consider to be basic physics

    [rant] Write a letter to the school board telling them that they were/are not properly preparing their students for what they need to know in the world.

    Graduates need to have enough science and math for a at least superficial understanding of DC and AC, watts and watt-hours, levers, center of gravity, using given math formulas, percentages, the difference between a bacterium and a virus, and enough chemistry to differentiate acids and alkalies in household compounds.

    Not as many people learn these things in US schools as used to. I watched my stepdaughter get through school without learning them (and she WOULD not learn them from ME). Other developed countries do a much better job of teaching the basics.
    [/rant]