electro22

conduit derate question

17 years ago

My garage currently has 1-1/4" PVC buried conduit running to it. That conduit houses (3) #4awg and (1) #6awg (ground) supplying a 100A sub-panel. I recently had solar panels installed on the garage and the contractor added the output wires of the solar inverter to the exiting conduit (solar inverter outputs 220v at a max of 15-20A). The solar output is on (3) #10awg and it shares the same ground as the existing 100A circuit. They put a 30A breaker on the solar wires. All wires (new and old) are THHN rated.

Based on my reading, it seems as if they should use a 20A breaker on the solar and may need to lower the sub-panel breaker to something less than 100A because of the derate required when running more than 3 current carrying conductors in the same conduit. Can anyone confirm what the appropriate breaker sizes are for this application?

Thanks for any insight!

Comments (4)

  • 17 years ago

    Re the solar output:

    Generally, output from PV systems has to be derated twice: once because it meets the conditions of a continuous load and second because PV arrays can exceed their rated values in cold weather. (Yes, COLD weather, which may seem counterintuitive.)

    Thus, the math would be: 20A x 1.25 (continuous load) x 1.25 (overproduction) or about 31.25 amps. A thirty amp breaker there is by no means too large.

    As to the "requirement" to derate wire ampacity when there are more than 3 current carrying conductors, the math starts with the full ampacity of the wire in free air, not the NEC ampacity rating in conduit conditions. As a practical matter, upsizing the conductors doesn't kick in until you've exceeded about eight.

    What may be an issue here, though, is the ampacity of the buss bars in the panel. It is my understanding that both potential feeds--the solar and the utility--have to be added together to ensure that the panel isn't overloaded. (Others may disagree with me on this and I'm not sure I'm 100% right about that.) But assuming I'm right, you might need to lower the breaker feeding the subpanel to 70 amps to meet code.

  • 17 years ago

    Hi - Thanks for the response. I should have mentioned previously that the solar inverter is not connected into the garage sub-panel. The garage inverter output goes into my basement then into sub-panel where it gets combined with another inverter (from panels on my house roof). From there, it goes to a meter to measure the output (utility requirement) and then into the main 200A panel for the house. So, the only relationship with the garage sub-panel and the solar inverter in the garage is that they share the conduit back to the house and the ground wire.
    Based on your understanding and this new info, would the garage still need a 70 amp breaker?

  • 17 years ago

    "I should have mentioned previously that the solar inverter is not connected into the garage sub-panel."

    Gotcha now. And I should not have assumed that it did. :-) I think it was the shared ground that led me astray.

    With three #4s and three #10s, you're fine with 1 1/4" conduit as far as fill requirements go. But it's the derating part that still has me scratching my head.

    For the purposes of derating, you start with what is sometimes called "full ampacity" which, for #4AWG copper is 95A (from 90C column), although the usual ampacity for the purposes of determining maximum overcurrent protection (breaker) for #4AWG used indoors in conduit or in a cable (60C) would require a 70A breaker.

    HOWEVER, there's a specific NEC table exception that permits #4 to feed a 100A panel within a residence.

    [That would tend to imply that your garage is attached and was considered part of the residence for the purposes of allowing #4 to feed a 100 amp subpanel in the first place.]

    To be perfectly honest with you, I don't know how this is reconciled in a derating situation. That is, if the presence of other wires in the same raceway triggers derating of #4 using 95A as the starting point, you've already crossed that threshold since it is being used as a 100A feeder. WTF?

    Perhaps someone who knows more than I do can give you a definitive answer to that question. (You reading along Petey? Brick?)

    Another thing that may or may not be an issue is the effect of having two power feeds in the same raceway from separately derived systems that are not yet merged, or the fact that the grounds appear to be bonded in a subpanel with no other inter-system connectivity. Again, though, I'm afraid that's above my pay grade.

    While I'm confident that you'd meet all derating requirements with a 70A breaker, I can't say with certainty that it's required.

  • 17 years ago

    Thanks again for all the info, its been very helpful. And you are correct, the ground from the garage inverter connects to the ground in the garage subpanel. We'll see if anyone else chimes in, if not, the safe path would be to use a 70A breaker. I really don't think I'll miss the extra 30A :)