Generator Problem

18 years ago

I recently bought a manual transfer switch and had it installed by a local electrician. It contains 8 - 110V circuits and 1 -220V circuit (a well pump). I fired up the generator and tried it out. All the 110 circuits work great. I can switch back and forth from utility to gen power. The well pump will not kick on however. The plate on the well pump say 1/2 HP - 6 amps. I have a 5000 watt generator with 6250 surge watts which should be more than enough to start the pump. When I switch the well pump to gen power (with no other circuits in use) the volt meters on the transfer switch show approx 2200 watts going to each side of the transfer switch. This continues for 20 or 30 seconds, then drops to zero and the pump does not start. Any idea of what the problem is?

Comments (5)

  • 18 years ago

    Your generator is probably a consumer grade model, and as such may have far less actual capacity than the sticker on the unit indicates. A more realistic rating for your set would be 4kw, and at that I would expect the voltage to be low.

    Simply put, you don't have enough generator capacity.

  • 18 years ago

    It is a consumer model (Coleman Powermate as sold in Home Depot), but I'd be very surprised that a relatively new 1/2 HP 6 amp well pump would require more than 4500 watts to start. The 120 circuits are producing 125 volts at 65 cycles according to the voltmeter

  • 18 years ago

    65hz is WAY out of spec if you have any electronics on there. my UPSs won't even charge their batteries at 65hz, they run fully on battery thinking there is a problem.

    the problem is your startup current for the pump motor. start current can be 5-10 times running current, if not more. your genny may not be able to handle this brief spike.

    also, have you double checked to make sure you get 240 volts to the pump? some gen sets do not provide 240, just 2 outputs of 120, but they are off the same leg of the windings. RV generators are like that. use a voltmeter and measure each leg to the other, if you read zero volts, read them to ground and you should read 120v. this would mean they are the same leg.

  • 18 years ago

    I'm using the 120/240 socket on the generator connected to the transfer switch using a cord supplied by the switch manuf (Connecticut-Electric) with the L14-30 connecters. I believe some generators have a 120/240 switch but this one does not. The transfer switch itself has 10 switches or circuits, 5 on the left hand side, 5 on the right hand side -the top 8 are used for 120 circuits, the bottom two ( 1 left - 1 right) are joined with a tie bar and provide 220V to the well pump. However I do not know if the 120 feeds to each side of the switch are out of phase (They should be, correct?) Perhaps I'll just get the electician back to check it out

  • 18 years ago

    Before you go any further, take davidandkasie up on his suggestion and measure the voltages on the legs. That will give you a much better indication of what may be wrong. It will answer your question regarding phase.