Using use-2 cable

11 years ago

I am installing a new sub panel in a barn, from my existing main house panel I am using un-jacketed 2-2-2-4 USE-2 cable run underground. Do I need it in conduit from the main panel to where it leaves the building, where it will be in the stud cavity? From there it is in 2" schedule 80 PVC into the ground, then direct burial at 24" deep. It has been suggested that I need to run it in conduit inside the stud spaces. Any help would be very much appreciated.