Detached Shop Building Wiring

10 years ago

Wanting to run electricity to my detached 10'x16' shop building. Might run a small window unit AC (5000BTU), small power tools, lights. Plan to use two 20A circuits installed in my main home load center. The lighting and one wall outlet on one circuit, and three wall outlets on the other circuit. About a 110' run to the shop, then each of the circuits will run about 20' max inside the shop. Have calculated voltage drop, and #10 wire will give about 4.5% drop. It's my understanding that #10 is acceptable for connection to the wall switch (lights) and wall outlets. Will this be adequate or do I need to install a sub-panel?

Comments (3)

  • 10 years ago

    The size of the wire has nothing to do with whether you need a subpanel or not.

    If you want to run more than one circuit to the building, it will need its own grounding system. However, you can install your "two 20A circuits" as one 20A multiwire branch circuit and that won't require a grounding system.

    The 5000 BTU/hr air conditioner will consume pretty much all of one 20A circuit.

    You need a ground between the two buildings under modern code in any event.

    How are you getting the wire between the buildings?

  • 10 years ago
    last modified: 10 years ago

    "The size of the wire has nothing to do with whether you need a subpanel or not."

    But if you put in a subpanel, it can effect the size of the disconnect, and then for all practical purposes, the size of the wire per 225.39. A panel can also effect whether or not you need a grounding electrode system.

    A subpanel changes the conductors between the house and shop into feeders instead of a branch circuit.

    Branch Circuit. The circuit conductors between the final overcurrent device protecting the circuit and the outlet(s).

    Branch Circuit, Multiwire. A branch circuit that consists of two or more ungrounded conductors that have a voltage between them, and a grounded conductor that has equal voltage between it and each ungrounded conductor of the circuit and that is connected to the neutral or grounded conductor of the system.

    Feeder. All circuit conductors between the service equipment, the source of a separately derived system, or other power supply source and the final branch-circuit overcurrent device.

    II. More Than One Building or Other Structure

    225.30 Number of Supplies.

    Where more than one building or other structure is on the same property and under single management, each additional building or other structure that is served by a branch circuit or feeder on the load side of the service disconnecting means shall be supplied by only one feeder or branch circuit unless permitted in 225.30(A) through (E). For the purpose of this section, a multiwire branch circuit shall be considered a single circuit.

    225.38 Disconnect Construction.

    Disconnecting means shall meet the requirements of 225.38(A) through (D).

    Exception: For garages and outbuildings on residential property, snap switches or sets of 3-way or 4-way snap switches shall be permitted as the disconnecting means.

    225.39 Rating of Disconnect.

    The feeder or branch-circuit disconnecting means shall have a rating of not less than the calculated load to be supplied, determined in accordance with Parts I and II of Article 220 for branch circuits, Part III or IV of Article 220 for feeders, or Part V of Article 220 for farm loads. Where the branch circuit or feeder disconnecting means consists of more than one switch or circuit breaker, as permitted by 225.33, combining the ratings of all the switches or circuit breakers for determining the rating of the disconnecting means shall be permitted. In no case shall the rating be lower than specified in 225.39(A), (B), (C), or (D).

    (A) One-Circuit Installation. For installations to supply only limited loads of a single branch circuit, the branch circuit disconnecting means shall have a rating of not less than 15 amperes.

    (B) Two-Circuit Installations. For installations consisting of not more than two 2-wire branch circuits, the feeder or branch-circuit disconnecting means shall have a rating of not less than 30 amperes.

    (C) One-Family Dwelling. For a one-family dwelling, the feeder disconnecting means shall have a rating of not less than 100 amperes, 3-wire.

    (D) All Others. For all other installations, the feeder or branch-circuit disconnecting means shall have a rating of not less than 60 amperes.

    250.32 Buildings or Structures Supplied by a Feeder(s) or Branch Circuit(s)

    (A) Grounding Electrode. Building(s) or structure(s) supplied by feeder(s) or branch circuit(s) shall have a grounding electrode or grounding electrode system installed in accordance with Part III of Article 250. The grounding electrode conductor(s) shall be connected in accordance with 250.32(B) or (C). Where there is no existing grounding electrode, the grounding electrode(s) required in 250.50 shall be installed.

    Exception: A grounding electrode shall not be required where only a single branch circuit, including a multiwire branch circuit, supplies the building or structure and the branch circuit includes an equipment grounding conductor for grounding the normally non–current-carrying metal parts of equipment.

    (B) Grounded Systems. For a grounded system at the separate building or structure, an equipment grounding conductor as described in 250.118 shall be run with the supply conductors and be connected to the building or structure disconnecting means and to the grounding electrode(s). The equipment grounding conductor shall be used for grounding or bonding of equipment, structures, or frames required to be grounded or bonded. The equipment grounding conductor shall be sized in accordance with 250.122. Any installed grounded conductor shall not be connected to the equipment grounding conductor or to the grounding electrode(s).

    Exception: For existing premises wiring systems only, the grounded conductor run with the supply to the building or structure shall be permitted to be connected to the building or structure disconnecting means and to the grounding electrode(s) and shall be used for grounding or bonding of equipment, structures, or frames required to be grounded or bonded where all the requirements of (1), (2), and (3) are met:

    (1) An equipment grounding conductor is not run with the supply to the building or structure.

    (2) There are no continuous metallic paths bonded to the grounding system in each building or structure involved.

    (3) Ground-fault protection of equipment has not been installed on the supply side of the feeder(s).

    Where the grounded conductor is used for grounding in accordance with the provision of this exception, the size of the grounded conductor shall not be smaller than the larger of either of the following:

    (1) That required by 220.61

    (2) That required by 250.122

    (D) Disconnecting Means Located in Separate Building or Structure on the Same Premises. Where one or more disconnecting means supply one or more additional buildings or structures under single management, and where these disconnecting means are located remote from those buildings or structures in accordance with the provisions of 225.32, Exception No. 1 and No. 2, 700.12(B)(6), 701.11(B)(5), or 702.11, all of the following conditions shall be met:

    (1) The connection of the grounded conductor to the grounding electrode, to normally non–current-carrying metal parts of equipment, or to the equipment grounding conductor at a separate building or structure shall not be made.

    (2) An equipment grounding conductor for grounding and bonding any normally non–current-carrying metal parts of equipment, interior metal piping systems, and building or structural metal frames is run with the circuit conductors to a separate building or structure and connected to existing grounding electrode(s) required in Part III of this article, or, where there are no existing electrodes, the grounding electrode(s) required in Part III of this article shall be installed where a separate building or structure is supplied by more than one branch circuit.

    (3) The connection between the equipment grounding conductor and the grounding electrode at a separate building or structure shall be made in a junction box, panelboard, or similar enclosure located immediately inside or outside the separate building or structure.

  • 10 years ago

    "It's my understanding that #10 is acceptable for connection to the wall switch (lights) and wall outlets. Will this be adequate or do I need to install a sub-panel?"

    Run #10 between the buildings, and install a double pole "snap switch" rated for 20 or 30 amps where the conductors enter the building. Then run #12 from there.

    225.31 Disconnecting Means. Means shall be provided for disconnecting all ungrounded conductors that supply or pass through the building or structure.

    225.32 Location. The disconnecting means shall be installed either inside or outside of the building or structure served or where the conductors pass through the building or structure. The disconnecting means shall be at a readily accessible location nearest the point of entrance of the conductors. For the purposes of this section, the requirements in 230.6 shall be utilized.