Working Space Clearances - Code

9 years ago
last modified: 9 years ago

Hello, I have a question about Electrical Code Article 110.26 relating to Working Space Clearances in front of electrical equipment. It specifies 3 feet in front of "live parts". My question relates to an outdoor electrical meter. Is this measurement from the front of the "meter socket" (in my lay term - the circular glass cover on the meter) which projects out about 3" from the metal box or from the front of the metal box of the utility meter?

Thanks for any help. We are doing some work and just want to know the code before we start outdoor renovations, so that we take our measurement from the correct point.

I am editing to add a photo. Is the 3 feet measured from the circular meter socket (with clear cover) or from the rectangular metal box?

Comments (10)

  • 9 years ago

    Thanks for replying

    from the rectangular box? It says "live parts" so I figured those live parts were in the meter and therefore would measure from front of round meter.

  • 9 years ago

    Most likely the meter itself is service equipment not covered by the code. You need to contact your power company as to what their requirements specifically are (usually they have a one or two page sheet on what they want to see).


    amaranthan thanked Ron Natalie
  • 9 years ago

    Thanks Ron. This is the drawing for code I'm referencing. I can't tell if the 3 feet is to the front of the meter itself or to the metal box. It's hard to tell where that arrow is pointing to. i.e. Is the meter a "live part"?

  • 9 years ago

    Note that it says the space increases to 4 feet for 151- 600 volts. Most homes have 240 volts coming in to the meter, so you would need 4 feet, not three. That being said, I'm not sure if that applies to meters. As Ron said, you really need to talk to the POCO to see what their requirements are.

    amaranthan thanked mushcreek
  • 9 years ago

    Thank you mush creek. I have talked to them. But my question where does the measurement start? At the meter (again my lay term of clear covered circular thing) or at the solid metal rectangular box?

    Thank you

  • 9 years ago

    I just met with electrical inspector. It's measured from the metal rectangular box.

    Thanks weedmeister you were correct.

  • 9 years ago

    Mushcreek, Is the voltage measured from ground or between conductors? I don't believe any wire on a 240 volt service is more than 120 volts (RMS) above ground.

  • 9 years ago

    In the case of that figure above which does come straight out of the National Electrical Code, they are talking voltage to ground. Your household 120/240 is indeed only 120V by that yardstick.

  • 9 years ago

    How many volts is in the transformer cabinet behind the meter socket?? ;D