Help me pick GFCI breakers for MWBC

7 years ago

I have a Siemens sub panel and am in the process of moving 2 MWBC over. My question is what is the appropriate breaker choice. I need a Siemens 15 amp double pole, GFCI, 120volt breaker. What about afci? Is nuisance tripping a real issue with that? Is there a combo breaker that would protect against both?

Comments (5)

  • 7 years ago

    It would entirely depend on what the circuits feed. Just about every living space these days requires AFCI by code. Unless you're feeding outside/garage/unfinished basements, why do you think you need GFCI? If you're feeding the kitchen countertops, laundry, or bathrooms, 15A is too small.

    I'm no fan of Siemens panels. I can't imagine why anybody in their right mind would install one given an option. Yes Siemens makes Dual Function AFCI/GFCI breakers (note avoid thinking that the word "combination" means that. Combination on AFCI just means it detects both series and parallel arc faults. Pretty much all the ones on the market these days are). The problem is they only make them in 15 and 20A SINGLE POLE BREAKERS. You can get two pole GFCIs and two pole AFCIs seperately. If you need both, you may be back to putting an AFCI in the panel and GFCI receptacle(s).

    I can't tell you what model number to use because you didn't state which panel you have. There are three "SIEMENS" breaker style depending on whether these are plug in or bolt on breaker and whether it's the traditional Siemens or a remarked Murray panel.

  • 7 years ago

    Ron, it’s a PL series sub panel. Picture attached.


  • 7 years ago

    So, why do you think you need a GFCI again?

  • 7 years ago

    My error. I think I should be looking for the AFCI breakers for the reasons you explain above. I’m protecting the living area not the kitchen or garage. I have 2 14-3 wire circuits with 2 hot and shared neutral. So what do you suggest for a 15 amp 2 pole AFCI 120v plug in breaker? Need a Siemens brand. I appreciate the help because I don’t want to order something that won’t work.

  • 7 years ago
    last modified: 7 years ago

    That's a P1 panel I think (not PL).

    B215AFC would seem to be the right one (2-pole, AFCI 15A). If you're just feeding regular lighting/receptacle circuits.