Outlets in a basement

17 years ago

We are finishing (albeit very slowly) our basement. We are using a Wallmate type product on exterior walls as opposed to framing. Wallmate is essentially 1.5" of XPS slotted vertically on each end so that when two 2 X 8 pieces are put together a channel is there to flush mount a 1 X 3 fur strip. You end up with fur strips 24" on center. Once the XPS is up you may frame right up against it or put drywall over it. I am considering just drywalling (NOT framing) and what the downsides of doing so with respect to installing wall outlets will be. I will need 3 outlets, all with 20 feet of each other spanning two perpendicular walls. Most other outlets/switches will be on framed interior walls and should not be a problem.

In the sections we are not framing they suggest cutting a whole in the XPS, mounting a block of pt wood on the concrete and an electrical box to the wood. You then use a router to create a vertical channel to run your wiring down to the electrical box. If I go with this method have a few questions:

1) Do they make 1.5" deep metal outlet boxes? The 2" and 21/4" deep tend will stick out too far thru the drywall. Also, are these shallower boxes typically up to code?

2) Is mounting these boxes to wood over concrete up to code? (I already have several mounted directly to concrete in my unfinished basement; likely put there when the home was build 20 years ago; IÂd think it better to install over a small block of pt wood).

3) I was told running regular conduit would NOT be up to code and that metal wrapped braided conduit would be required and is expensive. However, I noticed the outlets already in my basement have wiring that drops from the rafters into what looks like metal pipe that apparently somehow screwed into the outlet box. I think this is cheaper than that braided conduit stuffÂno? Is this up to code? Could I use this method with pipe in the channel cut into the XPS?

4) In this method, it appears you really can not have horizontal runs from outlet to outlet (I guess you could if you also removed a portion of the fur strip) but rather the wiring drops from the ceiling into the channels you cut in the XPS. Does this mean each wire has to come from a different circuit in the beaker box?

Any comments regarding code, safety, the best way to do this, the typical way to do this, cost, etc etc is appreciated. I have not called any electricians yetÂI want to have a general idea what I should be looking for first and what I might be in for? THANKS, I know this is a big post.

Comments (10)

  • 17 years ago

    1.5" is way to thin for any legal box.

    There's nothing that says you can't mount the box to a piece of wood or to the concrete directly. However, I feel you are not installing your WALLMATE to the manufacturer's recommendsations. You should be using a 2x3 furing strip if you are going to be putting electrical wiring in. This will give plenty of room for a normal box.

    The other problem you have here is that running NM cable just under the surface of the drywall isn't going to provide legal protection for it. You are supposed to put the cable in an channel routed in the back (the side AWAY from the drywall).

    I don't know why most listed conduits wouldn't do the job unless you have goofy local codes. Metal braided conduit sounds like flexible stuff. EMT or rigid would suffice as would AC cable.

    There's nothing that says you can't run the wiring up and down like you describe. Yes it makes it longer meaning you use more wire and if it gets way long you can run into voltage drop problems, but I suspect in your case it's not an issue. It does not require multiple circuits (breakers).

  • 17 years ago

    Thanks!
    Re:
    1.5" is way to thin for any legal box.

    I saw them at HD, the normal ones are 2" deep.

    Re:
    There's nothing that says you can't mount the box to a piece of wood or to the concrete directly. However, I feel you are not installing your WALLMATE to the manufacturer's recommendsations. You should be using a 2x3 furing strip if you are going to be putting electrical wiring in. This will give plenty of room for a normal box.

    You are correct. I had planned on framing this 9 foot section in front of the XPS that is why I used the 1 X 3 strips. I could pop them out and use 2 X 3s.

    RE:
    The other problem you have here is that running NM cable just under the surface of the drywall isn't going to provide legal protection for it. You are supposed to put the cable in an channel routed in the back (the side AWAY from the drywall). I don't know why most listed conduits wouldn't do the job unless you have goofy local codes. Metal braided conduit sounds like flexible stuff. EMT or rigid would suffice as would AC cable.

    Wallmate shows the notch in front as I recall, actually ther is a vertical 1/2" plus space between XPS and drywall...if using 2X3 fur strips. You would need to notch horizontally...and the becomes troublesome. Also, I also assume you mean the non metallic (regular) type wiring would need to be in the back side of the XPS...I assume metal coated braided etc is allowed to sit between the XPS and drywall....?

    Re:
    There's nothing that says you can't run the wiring up and down like you describe. Yes it makes it longer meaning you use more wire and if it gets way long you can run into voltage drop problems, but I suspect in your case it's not an issue. It does not require multiple circuits (breakers).

    Ignorance here but a wire comes from the box and goes down to the outlet and you are suggesting it goes back up and over to the next? Is that pipe type stuff that attaches to outlet box better than the metal conduit?? Safer? Cheaper?

    Perhaps I should just frame these small areas as originall intended...

  • 17 years ago

    Using a 4" square box with a mudring will work. The mudrings are available in 1/2" depth to accommodate the drywall thickness. Use metal conduit to protect the wiring if it will be less than 1.25" from the surface of the drywall.

  • 17 years ago

    "The other problem you have here is that running NM cable just under the surface of the drywall isn't going to provide legal protection for it."

    Where are you getting this from?
    NM requires protection in bored holes less than 1.25 from the face of the stud, but not just behind drywall.

    NM is run directly behind drywall all the time.

  • 17 years ago

    I assume NM is what a layman calls regular ole white wiring..?

    In this application I assume it can not be used because there is either no stud or if a 2 X 3 was used it is only providing 1/2" clearance to the drywall.

  • 17 years ago

    I don't see any reason for not using 4"sq x 1-1/2" boxes with 5/8" plaster/mud ring wouldn't work just fine.(5/8" ring for 1/2" drywall because if you measure a mud ring it actually measures from the back face not the front, then figure for the screw heads that actually hold the drywall out slightly, it beats shimming receptacles out to the drywall) I personally would just cut them into the insulation as shown in the install instructions, then anchor them to the concrete thru the 1/2" holes provided after you stand up the panels with some sleve or plastic anchors with the nm/romex channeled up to the top of the wall with enough extra to bring two or three together into a J-box with your receptacle circuit in it above the drop ceiling. I hope you are putting in a drop ceiling for ease of maintenance and access to your mechanical and electrical systems. Just a suggestion. It only takes one leaky pipe or adding one electrical device in the future to make you wish you had a drop ceiling. That is, of course, if you have adequate head room.

  • 17 years ago

    What does NM stand for..sorry for the ignorance. We WILL have a dropped ceiling!

  • 17 years ago

    on wikepedia one of the uses of nm is non-metalic.

  • 17 years ago

    NM is the NEC designation for Non-Metallic cable (sometimes called 'Romex' after a large manufacturer).

    AC is the designation for Armored Cable (slang reference as 'BX', even though BX is an old name for a different cable type without the bonding strip).

    MC is Metal Clad. Comes in a number of flavors some with spiral armor,some with welded Al tubing as the outer layer.

    EMT is Electrical Metallic Tubing (the thin walled stuff).